wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
The UL text clearly states that the receptacle is rated for use split-wired on a MWBC with the ungrounded tab removed. The definition of "voltage, nominal" clearly states that 120/240 is a voltage class.I don't see anything in that text that says that the receptacle is rated for the "voltage class" 120/240.
So the question just reduces to what voltage class to assign to an MWBC, 120, or 120/240? If the latter, then the UL text implies that the receptacle is rated for the "voltage class" 120/240.
Cheers, Wayne