A 3-wire MWBC is two 120 volt circuits. Why is that so hard to understand?
It's not that it's hard to understand your point of view. And if that is the industry consensus (more or less) then I'm not going to fight it. It's just that I don't think it's at all obvious from reading the code.
Article 100 (Note the definition of MWBC as a singular circuit.)
Branch Circuit, Multiwire. A branch circuit that consists
of two or more ungrounded conductors that have a voltage
between them, and a grounded conductor that has equal
voltage between it and each ungrounded conductor of the
circuit and that is connected to the neutral or grounded
conductor of the system.
Voltage (of a circuit). The greatest root-mean-square
(rms) (effective) difference of potential between any two
conductors of the circuit concerned.
That seems to pretty clearly define an MWBC as one circuit of 240V. We can find more...
210.4 Multiwire Branch Circuits.
(A) General. Branch circuits recognized by this article
shall be permitted as multiwire circuits. A multiwire circuit
shall be permitted to be considered as multiple circuits.
Note permitted, not required. (Emphasis added.)
(C) Line-to-Neutral Loads. Multiwire branch circuits
shall supply only line-to-neutral loads.
Exception No. 1: A multiwire branch circuit that supplies
only one utilization equipment.
So per the exception wording, two hots and a neutral that go to a single outlet are still an MWBC, and also still a single circuit. Per the voltage definition, this is a 240-volt circuit.
Granted, this is 'for the purpose of this section', but we now have multiple sections treating an MWBC as one circuit by the basic definition, vs. one section permitting it to be considered otherwise.225.30 Number of Supplies. [...] For the purpose of this section, a multiwire
branch circuit shall be considered a single circuit.
It just seems to me that 210.12 ought to say 'all 120V circuits, including MWBCs serving 120V outlets', if that's what it intends to mean. There's just too many other places in the code which imply that an MWBC is a single, 240V circuit. 210.12 needs it's own 'for the purposes of this section'. Or at any rate, people should not claim that the meaning should be bleedingly obvious to newbies.