I got to thinking about this 25ohm issue and thought of it this way:
I thought of 2 parallel paths, one with 25 ohms is resistance and the other with less. The the same voltage is applied across which one would have more current flow through? The increase the voltage and even more current would flow. I realized that it is in our best interest to assure that the resistance of the ground rod should be as low as we are able to get because should another path to ground occur it would be that path where the current to ground be greater than that path to ground via the ground rod itself. As the potential to ground is increased as a result of a lightning strike which path to ground may be more favorable, the ground rod or another path that has less? Of course that second path to ground may not be present under normal conditions but but what would be the result if one unintentional ground should occur?
This is theoretical at best seems to be a reasonable to justify why it would be important to reduce the grounding resistance. Why was 25ohms selected as the standard? Good question though.
The problem is that just because we have two rods, lets say both is 50 ohms, but they will not act like a single rod of 25 ohms and each will have separate shells and they do not reduce the resistance in the way we think when paralleling two resistors, this is because of the earth between the shells of the rod do not add up because each is its separate entity that is reference to the X/0 or center tap of the transformer and the MGN and miles of other reference points in the utilities supply system, when two rods are withing the sphere of influence or the other rod, it will reduce the resistance very little because you have not added any larger parallel paths for the current to flow,you are still within the area of soil of the first rod and have only added another connection to this same soil, this would be like taking a resistor and making another connection to it and expecting a lower reading from the same end of the resistor, with soil you might increase the surface of the connection to the resistor but you still have the same resistor.
The problem is that as I pointed out in the other post, a ground rod can only serve as a protection device if it was to be able to consistently open the OCPD, but we know it can not be depended upon this function as it is in many cases impossible to get a low enough resistance to consistently do this, as far a stopping step potential, if the ground rod can't not open the OCPD then it will sit there with the full applied voltage with the voltage dropping off drastically within the first few feet of the rod, and in most soils this would have a 75% or 90 volt drop that a person contacting these two points would receive this voltage across there body, now if the ground rod is remote from other metallic paths that are bonded to this ground rod then the difference of potential can be the full 120 volts because even at 12' from a rod you will start getting to the 98% of voltage drop, take a simple trailer such as the Coke a Cola concession stand in the thread that was linked to in the first post of the "Time to Eat Crow" thread, even if a ground rod was used and the EGC was not connected and there was a fault, if this ground rod was on the back side of the trailer away from the ordering window, the shell of this trailer could be as high or close to the full 120 volts to earth at this point, and a person who might be bare footed could be harmed, if the ground rod can not provide a fault path with a low enough impedance to open the breaker then it can not provide any protection from voltage to earth known as step potential.
It is simply because the earth that has more parallel paths the farther you get from the rod that will maintain the 0 volt reference to the transformer center tap or X/0 then the rod has the ability to bring the soil around the rod to the same potential of the rod because the rod only has a few parallel paths.
It doesn't matter the source of the voltage, a corner grounded 480 volt system will still have the same 75% voltage drop at the 3' shell from the rod it will just be a higher voltage or 380 volts, lightning striking something grounded to the rod while most of the energy will flow and other paths, the voltage left over will still drop across the earth around the rod at the same rate, so again the rod would not provide any protection from step potential even in a lightning strike, and because of the high frequency nature of lightning most of the current will flow on other paths.