Timbert
- Makawao, Hawaii
While it's true that the air is thinner (less dense) than compared to sea level. Most electronics are designed to operate to at least 1000 m without de-rating, therefore you only need to consider the difference from the reference altitude to your actual altitude. So, a piece of equipment with 1000 m service ceiling is only 2000 m above that.It's certainly better than not derating at all, but I wouldn't say it's "conservative", just adequate. At 3000 m altitude, there are 26% fewer air molecules in a given volume of air than at sea level.
It looks like you used density for you calculation to get 26% difference form 0 to 3000 m, but at 1000 m the difference in density is already over 9%. So, the difference from the normal operating condition (1000 m or less) is only 17%.
Also, not all heat is lost as a result of convection, some is lost through radiation and conduction. As I mentioned before lower ambient temperatures (typically 2C for each 1000 m) can also be used to your advantage.