I would like to ask for information, experiences, recommendations, and whatever I can get on the issue of the use of aluminum (AL) conductors. The NEC has allowed AL conductors for a very long time. The Department of Defense (my present employer) publishes its own “building codes” in the form of “Unified Facility Criteria (UFCs).” The relevant UFC allows AL conductors above a certain AWG size. I am dealing with a military base that has adopted an even more stringent requirement: “copper only.” I would like to get them to reconsider that requirement. But it would help if I could present some supporting technical substantiation.
Questions:
- Am I right in believing that AL conductors had a bad reputation in decades past, and that the technical issues included poor electrical connections, special requirements for making those connections, corrosion, and overheating to the point of creating a fire hazard?
- Am I right in believing that those issues have long since been resolved, and there is no longer any reason to be concerned over the safety of using AL?
- If use of AL conductors is safer now than in decades past, what has changed? Is it something to do with manufacturing (i.e., materials science)? Is it related to installation techniques?
- If AL is used for, say, service or feeder conductors, will that require periodic maintenance to ensure that the connections remain tight?
- Do you use AL conductors when you are given the option?
- Are you aware of any recent failures (e.g., fires) for which the cause was traced to AL conductors?
- What else should I know about AL conductors?
Charlie, I am answering your questions first before reading all the other replies, as they are numerous, but I feel I can offer reasonable and logical answers since I have done lots of research on this subject over the years. Early in my career, I worked for an EC who did alot of service work on mobile homes (and I mean the old “mobile homes”-you know, the ones that caught fire and burned down Before the FD even showed up) where we would replace receps and fixtures on old AL romex. The Codes decision to ban the use of AL under #10 is most definitely the right call-even with new manufacturing in place since the 80s. AL that small is too easy to have issues.
That being said, in the early 80s when AL was getting a bad wrap for anything (feeders, branch circuits, services, you name it), obviously ALCO and all the other foundries didn’t want to lose that business. They went to their engineers and chemists and came up with the AA8000-an ALLOY, not straight AL. With this alloy, the wire became stronger than AL, lighter than the original, more durable when it came to expansion and contraction, and much better workability. If there was truly any more danger in using it, certainly the Code would not have allowed its use in any way shape or form. Yet, they did, as long as it was the alloy-not straight AL. And since the 80s theres been even more modifications and improvements that personally, I prefer it to copper for all our feeders and larger branch circuits.
Look at it this way: almost all utility feeders, whether through the air in tri/quad plex or underground in conduit or DB and even their transmission wires, are almost exclusively AL alloy or a mix with steel. Theres literally hundreds of thousands of miles of AL wire installed that fares totally fine in many extreme environments. MOST faults that do happen with AL could happen the same way for copper.
NECA/IBEW has their written installation standard about the proper use and installation of AL wire and there is no major disqualifications in using AL wire.
Most terminals, lugs, breakers, etc, carry a dual rating these days, leaving the possibility of installing AL to the wrong lug a thing of the past.
As with all trades and specifically electrical, proper installation following manufacture’s/Code requirements and industry best practice is the best way to ensure a safe and compliant installation. You can install a copper wire wrong and burn a house down just as much an AL feeder if you install it wrong or don’t follow code. One of the biggest installation hazards is guys “ringing” the conductor insulation-this is a major no-no! Not just for general wire installation, but especially for AL. It should always be “skinned” with a sharp knife or the use of a proper stripping tool for AL only.
We install alot of large gens for emergency backup. We pull AL feeders and cables all the time, unless copper is specifically called out. Only time theres an issue is when one of my guys is dumb enough not to use a torque wrench. Its cheaper, lighter and in larger sizes, much easier to work with compared to copper.
Along with that: just like ANY other electrical installation, periodic inspection and/or testing is important and required. Obviously NFPA 70B talks about alot of equipment industry standard and best practices for this. Even on resi meter combos, the mfr has their inspection and cleaning reqs. But honestly, how many homeowners do that or wanna pay us to come do it for them? Id say less than 5% in the whole continent. Even with that, Ive never heard of a fire due to AL wire failing in the last 20 years that wasn’t from an installation failure or a mfr defect. And each of those could happen to copper as well.
All in all, I know this post is long, but to put it short: outside of a few rare cases, mainly industrial applications, would I have a hard time sleeping at night after I installed AL wires to a panel or piece of equipment. If I do my research thoroughly on a product and get trained and have experience in its use and installation, there should be no problems at all with AL wire used in todays electrical systems.