160226-2119 EST
iwire:
Your statement is probably correct that the Fluke may not be fast enough to measure the very short peak inrush cuirrent that doesn't exist, but also it may not be fast enough to measure the maximum of several cycles of the motor starting currrent.
So I ran an experiment with my Fluke 27 that is at home. With my test motor there is about 6 cycles of startup current at about 123 V. Using this test motor as a signal source, and an LEM Hall sensor the scope read a peak of 5 V ( 5 V = 100 A ). Convert this to RMS and the Fluke, on AC, should have read 3.5 V, but the maximum reading was 0.88 V. This is 25% of what it should have read. Thus, I would estimate the Fluke 27 averaging time is around 0.5 second. Way too short for measuring this startup current signal.
For motor starting current we need an averaging time of 16 to 32 milliseconds. But that is not fast enough for transformer inrush. Here we need something in the fractional millisecond range.
.
iwire:
Your statement is probably correct that the Fluke may not be fast enough to measure the very short peak inrush cuirrent that doesn't exist, but also it may not be fast enough to measure the maximum of several cycles of the motor starting currrent.
So I ran an experiment with my Fluke 27 that is at home. With my test motor there is about 6 cycles of startup current at about 123 V. Using this test motor as a signal source, and an LEM Hall sensor the scope read a peak of 5 V ( 5 V = 100 A ). Convert this to RMS and the Fluke, on AC, should have read 3.5 V, but the maximum reading was 0.88 V. This is 25% of what it should have read. Thus, I would estimate the Fluke 27 averaging time is around 0.5 second. Way too short for measuring this startup current signal.
For motor starting current we need an averaging time of 16 to 32 milliseconds. But that is not fast enough for transformer inrush. Here we need something in the fractional millisecond range.
.