The ground rod will help the pole deal with a lightning strike, but bonding the pole to the source is the only thing that will prevent electrocution from a ground fault.
As for installing a ground rod, don't most poles already have a concrete encased electrode as their base? If you want to require grounding of light poles it would probably be better to just require a connection to the rebar or mesh thats already there rather than trying to add a new rod. It might not meet the 20' foot rule, or use mesh rather than rebar but I wonder if it might make a better GE than a driven rod. Besides, where would you put the rod? Someplace where it might be subject to damage?
[ December 27, 2004, 11:32 AM: Message edited by: petersonra ]
I don't see how this would solve the problem. Driving a ground rod would not cause those who are responsible to maintain these structures to actually do so. Nor would it likely cause an OCPD to trip in the event of a ground fault.Originally posted by charlie tuna:
i think the national electrical code should consider evaluating the practice (and the practibility) of installing ground rods at poles.
one life is too many to loose when it can be prevented, and prevented by reducing job installation and maintainance costs. it may also help to educate people about grounding and bonding!
The ground rod will help the pole deal with a lightning strike, but bonding the pole to the source is the only thing that will prevent electrocution from a ground fault.
As for installing a ground rod, don't most poles already have a concrete encased electrode as their base? If you want to require grounding of light poles it would probably be better to just require a connection to the rebar or mesh thats already there rather than trying to add a new rod. It might not meet the 20' foot rule, or use mesh rather than rebar but I wonder if it might make a better GE than a driven rod. Besides, where would you put the rod? Someplace where it might be subject to damage?