Re: another electricution - metal street pole-baltimore!
Bob, that is interesting that you brought that up. I used to tell my apprentices the same thing, you may ground the secondary of two winding transformer or a 3? transformer one time and one time only
anywhere and it will still work.
It may not meet the requirements of the Code, but it will still work.
For instance, a 480Y/277V, 3?, 4w transformer could have one of its phases grounded and used in that manner. You would measure 480V between each phase and 277V to the neutral, no different than any other 480V system of the same configuration. However, from the grounded conductor to the neutral, you would measure 277V and also from the other two phase to ground would be 480V. </font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Will it work? Yes</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Does it meet Code? No</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Is it safe? No, because you have set up a trap that would kill someone and equipment is not made for that configuration.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">Then I went on to explain how a 480Y/277V, 3?, 4w transformer can have one of the phases grounded in the same manner and still meet Code by not bringing out the neutral conductor to be used as a neutral or grounding it (it
must be ungrounded). Since only the three phase wires are available, it can be used as either a three wire delta or a grounded phase delta if you ground one of the phases.