Direct bury mobile home feeder cable is available at any good electrical supply house.I just meet the inspector, good and professional man. He approved to go from the meter/disconnect directly to a new panel in the Mobile Home, eliminating the pedestal but going with new 4 insulated conductors from the meter. He mentioned that he needs to inspect the conduit, but I am wondering if I can use anything 4 conductors without going in conduit. At the service panel I will separate N/G and run the rods and the frame bond from there. Any input?
Yes, you have to protect the wire coming out of the ground.Didn't know, no experience with MH. Feeder is 100 amps. Can it be partially in the conduit? From meter to ground and from ground to panel.
Also, even as he approved in going from meter to panel, I am not comfortable bypassing a pedestal. He also stated that I don't need to go to Arc fault breakers as I am no replacing any circuitry, only the panel ... Does this make sense?
He approved to go from the meter/"disconnect"
At the service panel I will separate N/G and run the rods Any input?
At the service panel I will separate N/G and run the rods and the frame bond from there. Any input?
Also, even as he approved in going from meter to panel, I am not comfortable bypassing a pedestal. He also stated that I don't need to go to Arc fault breakers as I am no replacing any circuitry, only the panel ... Does this make sense?
I just meet the inspector, good and professional man. He approved to go from the meter/disconnect directly to a new panel in the Mobile Home, eliminating the pedestal but going with new 4 insulated conductors from the meter. He mentioned that he needs to inspect the conduit, but I am wondering if I can use anything 4 conductors without going in conduit. At the service panel I will separate N/G and run the rods and the frame bond from there. Any input?
IMO it is still subject to condemnation if deemed unsafe, but otherwise how can it be "wrong" if there was no "right" at initial installation? Some places have had codes/enforcement long before others so this will vary from place to place.That is not the opinion that I got from the state a few years back. But that's another discussion.
2nd point if nothing was codified and it is existing IMHO it is grandfathered. Thoughts?
IMO it is still subject to condemnation if deemed unsafe, but otherwise how can it be "wrong" if there was no "right" at initial installation? Some places have had codes/enforcement long before others so this will vary from place to place.
One example, around here you run into a lot of old farm houses that had initial wiring installed in 1930's and 40's as a result of the Rural Elecrification Act. There was a lot of work done that maybe did not meet NEC at the time, but there was no code authority or inspectors at the time in the area to enforce anything either - were those in violation of anything if there is no rule to violate?
IMO it is still subject to condemnation if deemed unsafe, but otherwise how can it be "wrong" if there was no "right" at initial installation? Some places have had codes/enforcement long before others so this will vary from place to place.
One example, around here you run into a lot of old farm houses that had initial wiring installed in 1930's and 40's as a result of the Rural Elecrification Act. There was a lot of work done that maybe did not meet NEC at the time, but there was no code authority or inspectors at the time in the area to enforce anything either - were those in violation of anything if there is no rule to violate?
Agreed.
You have an existing installation. That means it is grandfathered unless you touch it.
Only if it was code compliant at the time of installation.
That is not the opinion that I got from the state a few years back. But that's another discussion.
2nd point if nothing was codified and it is existing IMHO it is grandfathered. Thoughts?
That?s interesting;
The first service I had installed back in 1985 was done by an older gentleman who had been doing electrical inspections for 32 years.
I have seen manufactures instructions for mobile homes for early 1970 models, I think, that mobile homes started coming onto the market in the mid 1950?s not sure but I?ll bet even the early versions had installation guides.
I think it is a stretch to believe that the service installation for even an early 1970?s model was not inspected by an electrical inspection agency listed with the local utility.
As I said in my previous post:
There is a conduit, large enough, going from the Meter/Disconnect to the J-Box (the one closed to the ground) and another conduit going from the same J-Box to the MH (partially, as it is no going completely to the inside panel but I can add conduit to it).
Can I use or is recommend to use those existing conduits and use this J-Box as a pull box?
No, because it is too close to the ground?
No, because I can bother this nice Inspector? (I forgot to ask him)
It really will save time and money as you know everything is donated. I have a 250? of 4 AWG that I can donate for this 100 amps service (I will tape green the grounding).