I kept wondering why you are so vested in this seeming unreasonable position.
The more you posted on this subject the clearer it became. You believed and it seems still do believe, that there is no difference between stick built and mobile home rules when it comes to the electrical supply requirements.
You also believe in June of 1976 HUD took a position that mobile homes and manufacture homes are the same. You are so vested in this position because you done over a thousand electrical inspections with this point of view. According to your statement that was just the ones after the year 2000.
You are stating from the outside 3-wire to the manufactured installed distribution panel
Then you have your repeated statement prior to 2008 and a separate structure. At first I didn?t understand why you kept putting emphasis on prior to 2008. Then it hit me you came on board requiring a four wire feeder into the mobile/manufactured home when feeding its distrubution panel from another structure. Not because article 550 required it all along, but because 3 wire feeder became absolute by other sections of the code. So that tells me in your way of thinking there is still no difference between stick built homes than manufactured homes.
You keep saying a three wire feeder is safe, you need to quit advising the OP until you recognize article 550 rules when supplied by a feeder always required a four wire feeder to the distribution panel and you cannot deem the installation safe until it meets the min. requirements as outlined in article 550.
550.33(A)
Exception: For an existing feeder that is installed between
the service equipment and a disconnecting means as covered
in 550.32(A), it shall be permitted to omit the equipment
grounding conductor where the grounded circuit conductor
is grounded at the disconnecting means in accordance with
250.32(B) Exception.
What is unsafe about a 3-wire with no paralleled paths and bonded in the panel? Other than we can not do it in new work?
Anything wrong with this?