and technically speaking, on a job like this, for austerity's sake, you should probably go through and check every outlet to insure that someone did not combine the grounds and neutrals.
Remove bonding jumper at the service (temporarily for testing) and any wrongfully installed bonding jumpers at feeder panels. Keep everything else that is supposed to be bonded connected. If there are no other (accidenta or intentional) neutral to ground connections you should not see any continuity between the two. If you do there is a bond between them somewhere that should not be there - your task then is to find it. First places to look that are common problem areas is ranges and dryers. - simply unplugging them is a quick way to eliminate them from the continuity test. All it takes is for the occupant to get a new (or used) range or dryer and have the bonding jumper from neutral to frame left connected and you now have compromised the entire grounding system of the mobile home as neutral current can flow from the appliance neutral terminal to all items connected to the equipment ground conductor. Should the feeder neutral be damaged the EGC ends up becoming the neutral but nobody even knows anything is wrong for the most part.No coffee yet and mind is clogged! Should I remove the bonding jumper AND the frame (mobile home) bonding as well? And is not continuity ... attach the frame jumper and do a test
again?
Another mobile home in distress. See photos. Meter and 100 breaker disconnect is located less than 30' from the MH. The MH "disconnect" is now a junction box, no ground (only 3 conductors) and the inside panel has the neutral & ground tie together and are bonded only to the frame of the MH and no rods/electrodes.
Because the disconnect at the meter is less than 30', can I legally for a mobile home use the inside panel as a main and bond it to the 2 rods and leave, after cleaning the junction box as it is now? The photo shows the inside Federal Pacific (oh, oh) that I plan to clean and organize as the bus looks in good condition. Another low income situation. Sorry for many question, but been new in WA, new with NEC 2014, new with WAC and doing MH with very little money is no fun.
In another note: if a regular person read all topics posted in the forum (thousands) that person will be super qualify for a Master License!
can I legally for a mobile home use the inside panel as a main and bond it to the 2 rods and leave, after cleaning the junction box as it is now?
If I understand your question yes. ... Even that this is a mobile home, metal frame, etc.?
I am assuming that this is a pre 2008 NEC installation. Correct? Oh, yes ...
For your own reasons I guess so, to find out if neutral conductors are connected to EGC or other bonding conductors it really doesn't matter, there should be no continuity between "grounded" and "grounding" on load side of service equipment if the bonding jumper is removed.Thank kwired, but shouldn't I remove the frame bonding, and test it with and without?
I would need to look up current editions but I seem to recall wording in there at one time that allowed to mount service equipment on the mobile home if the home were placed on a "permanent foundation". I recall words of a State inspector as the AHJ interpretation of "permanent foundation" would mean a typical footing and foundation for support of the structure like you would find on other "on site" constructed buildings. Typically the transport axles would need removed and the structure need to be anchored to the foundation - not to a typical earth anchor. Simple stacked cinder blocks with facade "skirting" (no matter how nice it may look) is not a permanent foundation.can I legally for a mobile home use the inside panel as a main and bond it to the 2 rods and leave, after cleaning the junction box as it is now?
If I understand your question yes. ... Even that this is a mobile home, metal frame, etc.?
I am assuming that this is a pre 2008 NEC installation. Correct? Oh, yes ...
For your own reasons I guess so, to find out if neutral conductors are connected to EGC or other bonding conductors it really doesn't matter, there should be no continuity between "grounded" and "grounding" on load side of service equipment if the bonding jumper is removed.
I would need to look up current editions but I seem to recall wording in there at one time that allowed to mount service equipment on the mobile home if the home were placed on a "permanent foundation". I recall words of a State inspector as the AHJ interpretation of "permanent foundation" would mean a typical footing and foundation for support of the structure like you would find on other "on site" constructed buildings. Typically the transport axles would need removed and the structure need to be anchored to the foundation - not to a typical earth anchor. Simple stacked cinder blocks with facade "skirting" (no matter how nice it may look) is not a permanent foundation.
OK.550.32 (B) that would be allowed for manufactured homes the allowance did not apply to mobile homes 550.32 (A)
"Situation: a very old mobile home permanently installed at the site"
If I understand your question yes.
I am assuming that this is a pre 2008 NEC installation. Correct?
OK.
Some manufactured homes are not all that easy to tell apart from a mobile home - you do need to look at the home's "nameplate" to know what you have.
And to help complicate things there is this statement in the definition of Mobile home in 550.2:
"For the purpose of this Code and unless otherwise indicated, the term mobile home includes manufactured homes."
True but I believed him to be asking about an old mobile home. All the older mobile homes around here have a metal siding and an arched roof.
We did not see vinyl siding and pitched roofs until the manufactured homes came along
Mike I understand the question to be in regards to the interior panel ( distribution panel) 550.11 (A).
I do not believe he is talking about service equipment 550.32 (C)