Per the 2011 NEC section 314.28 (A)(1) and (2)
"Where splices or where angle or U pulls are made, the distance between each raceway entry into the box or conduit body and the opposite wall of the box or conduit body shall not be less than six times the trade size of the largest raceway".
Same goes for straight pulls except it is 8 times the diameter of the largest raceway.
This means for example that a 3" C would have to have at least 24" between raceways, and an LB would have to have at least 18" between raceways.
Sounds like the standard condulets can't be used any more and everything will have to be mogul. I recently saw this enforced on a job, AFTER the conductors were in place!!
"Where splices or where angle or U pulls are made, the distance between each raceway entry into the box or conduit body and the opposite wall of the box or conduit body shall not be less than six times the trade size of the largest raceway".
Same goes for straight pulls except it is 8 times the diameter of the largest raceway.
This means for example that a 3" C would have to have at least 24" between raceways, and an LB would have to have at least 18" between raceways.
Sounds like the standard condulets can't be used any more and everything will have to be mogul. I recently saw this enforced on a job, AFTER the conductors were in place!!