Ohh! I see you are referring to the 2011 NEC...
...but I don't see you point relative to the issue (an other-than-sole connection of a GEC to an electrode). The only one(s) I can think of is bonding to the water pipe or structural steel electrode to establish an SDS GES (these are more common acronyms
)... but I was referring to an other-than-sole GEC connection from the same system. And the gist of the matter is that bonding jumper connections count when considering the "sole connection" condition.
My point is I think it is "pointless" to require a conductor larger than 6 AWG from the first rod electrode to another rod electrode. Given the fact that if you choose via [250.53(A)(2)(1) as your supplemental option that at that point the 25 ohms is not an issue with the NEC. While we all can agree that [250.66(A)] allows the installation of a 6 AWG to the GE, which in this case is a rod type. The reference in [250.53(C)] to [250.66] doe lend you to using the table since the sole connection statement in [250.66(A)] will limit you to not use that allowance. However, I don't think (my personal opinion ) that this is what it is trying to say....again agree to disagree if you wish.
I revert back to the IRC on this as a higher supporting document under most jurisdictions to give you the following:
E3608.3 Rod, pipe and plate electrode requirements. Where practicable, rod, pipe and plate electrodes shall be embedded below permanent moisture level. Such electrodes shall be free from nonconductive coatings such as paint or enamel. Where more than one such electrode is used, each electrode of one grounding system shall be not less than 6 feet (1829 mm) from any other electrode of another grounding system. Two or more grounding electrodes that are effectively bonded together shall be considered as a single grounding electrode system. That portion of a bonding jumper that is the sole connection to a rod, pipe or plate electrode shall not be required to be larger than 6 AWG copper or 4 AWG aluminum wire.
TABLE E3603.1 SERVICE CONDUCTOR AND GROUNDING ELECTRODE CONDUCTOR SIZING
Which will call for a 4 AWG CU to a 200A Service....just for an example and will also reference (d) below as to the sizing of the GEC.
d. Where the sole grounding electrode system is a ground rod or pipe as covered in Section E3608.2, the grounding electrode conductor shall not be required to be larger than 6 AWG copper or 4 AWG aluminum. Where the sole grounding electrode system is the footing steel as covered in Section E3608.1.2, the grounding electrode conductor shall not be required to be larger than 4 AWG copper conductor.
E3608.2 Bonding jumper. The bonding jumper(s) used to connect the grounding electrodes together to form the grounding electrode system shall be installed in accordance with Sections E3610.2, and E3610.3, shall be sized in accordance with Section E3603.4, and shall be connected in the manner specified in Section E3611.1.
So in my view ( if I am like...fighting in court or something...lol ) I would argue the "sole grounding electrode system" as stated above and the verbiage that says when the two rods are tied together they are considered a single grounding electrode system [250.53(B)]...then Mr. Judge I think I am meeting the intent ...so that is one way of using code logic to present it.
Anyway....you get my point....sometimes as inspectors we have use common sense and push through the mud.