M. D. said:and if it is GfCI protected it can be real close to the tub,... just can't be directly over it ..:grin:
By saying "can't be directly over it" you mean can't be directly over the bathtub stall, then you're 100% right
David
M. D. said:and if it is GfCI protected it can be real close to the tub,... just can't be directly over it ..:grin:
dnem said:By saying "can't be directly over it" you mean can't be directly over the bathtub stall, then you're 100% right![]()
David
Dennis Alwon said:As far as I am concerned the receptacle is not over the tub unless it is in the ceiling. At what point would a receptacle over the edge of the tub be far enough away. If I had a 3' wide deck on one side, 8' , 10' -- get my point. This article definitely needs a rewrite in 2011. Any volunteers???
Kontrols said:Well, I didn't expect things to be so chaotic in here.
First of all 680.70 - 680.71 does apply, read the definition of a hydromassage bathtub in 680.2 I am personally shocked anyone would doubt the application......
Mike03a3 said:What about this tub?
I would say a receptacle in the tile, or the wall above the tile, in this picture would not be allowed. This particular tub does go all the way to the wall, unlike the one in the OP.
Mike03a3 said:What about this tub?
I would say a receptacle in the tile, or the wall above the tile, in this picture would not be allowed. This particular tub does go all the way to the wall, unlike the one in the OP.
Kontrols said:First of all 680.70 - 680.71 does apply, read the definition of a hydromassage bathtub in 680.2 I am personally shocked anyone would doubt the application.
M. D. said:BATHTUBSTALL
QUOTE]
Now you're talking!!!
M. D. said:I want to know if David would allow a gfci protected receptacle outlet on the outside wall behind those twigs just to the left of the window next to the bathtubstall
lpelectric said:Panel Statement:
The panel does not agree that receptacles need to be installed 3 feet away from the outer edge of a tub or shower. In many instances, especially in the smaller apartment sized bathrooms, it would be impossible to install a receptacle beyond 3 feet from the edge of the tub.
The panel does agree that receptacles shall not be installed within the footprint of a tub or shower. The panel action adequately conveys the location restriction without the use of a fine print note. The panel does not concur with the submitter's statement regarding the use of words with the same meaning to avoid redundancy.
Number Eligible to Vote: 10
Ballot Results: Affirmative: 10
The word "footprint" used in the CMP substantiation works for me. To me, this word is very descriptive. I just think of my own footprint when I walk. The area around my footstep is not included in my footstep. This means that the area around a tub is not included. It is only the tub itself.
No matter what I would like the code to say, it says what it says. :smile: