M. D. said:David the tubstall was kinda a joke there the word stall describes the shower the use of the word "or" indicates a choice between the two a bathtub or a shower stall.![]()
I understand that is your interpretation
M. D. said:David the tubstall was kinda a joke there the word stall describes the shower the use of the word "or" indicates a choice between the two a bathtub or a shower stall.![]()
sandsnow said:
You may get some agreement for a change . . .lpelectric said:I live in my own little world
406.8(C)Bathtub and shower space. Receptacles shall not be installed within or directly over a bathtub or shower stall.
(This is the way this sentence is constructed. The word "or" denotes a choice.)
Perhaps it would have been better to have worded it this way, but the CMP has not done so:
406.8(C)Bathtub and shower space. Receptacles shall not be installed within or directly over a bathtub enclosure or shower stall.
So, point being, the "common sense" "safe" way is IMHO this "interpretation": <snip>
M. D. said:To David and Ipelectric All I can say is,... Good grief:smile:
If you don't like what it says propose a change ,.. be prepared and have a measurement in mind .. Directly over means what it means whether you like it or not and the panel knows they can be right up to that boarder between over and directly over
Mike03a3 said:Don't try and link words on opposite sides of the "or".
Substantiation:The word area is much needed clarification in this section
for consistency. Section 410.4(D) is not a definition. It is more appropriate to
use dimensions and use the word ?zone? as this word is used in the rule twice.
This is only an editorial adjustment to the proposed new FPN. I agree with theconcept of this proposal.
Panel Meeting Action: Reject
Panel Statement:The panel recognizes that there is inconsistency between
the wording used in 406.8(C) and 410.4(D). This inconsistency is intentional
to differentiate the requirements for receptacles from the requirements for luminaires.
The panel does not agree that receptacles need to be installed 3 feet away from the outer edge of a tub or shower. In many instances, especially in thesmaller apartment sized bathrooms, it would be impossible to install a receptacle beyond 3 feet from the edge of the tub. It should be noted that receptacles installed in bathrooms are required to be GFCI protected whereas luminaires are not.
The panel agrees that receptacles shall not be installed within the footprint of a tub or shower from floor to ceiling.
Number Eligible to Vote:10
Ballot Results:Affirmative: 10
I see this as NOT above the tub. Say I was in the tub and had a bottle of shampoo...I just poured some on my head and set the bottle down BEHIND the faucet. Did I set the bottle "Above" the tub? No it's BEHIND the faucet that is NEXT to the tub (as it is not part of the tub). So now the outlet is ABOVE the bottle that is BEHIND the faucet that is NEXT to the tub.mistermudd said:![]()
If you were an inspector how would you call this one? Bath tub is to the right. And if you had to move the receptacle where would you put it?
My first picture I hope it works.
Chris6245 said:......P.S. By the way, isn't that receptacle upside down?:grin:
quogueelectric said:You automatically switched it off when water was in the tub??
quogueelectric said:Low voltage just like some hottubs have to make sure the tub is not empty. Remotely shutting off the power to the outlet until the tub is once again empty Therefore eliminating the shock hazzard.
Chris6245 said:P.S. By the way, isn't that receptacle upside down?:grin: