I think we need to be clear that 'fixture wires' need to be of a type listed in Table 402.3.
THHN, THWN, TW, RHW etc are not listed in that table.
In other words, the conductors we normally have on hand can not be used as 'fixture wires'.
402.3 Types.
Fixture wires shall be of a type listed in Table 402.3, and they shall comply with all requirements of that table. The fixture wires listed in Table 402.3 are all suitable for service at 600 volts, nominal, unless otherwise specified.
THHN, THWN, TW, RHW etc are not listed in that table.
In other words, the conductors we normally have on hand can not be used as 'fixture wires'.