Per 250.6, you wouldn't have, or would eliminate a parallel path with regard to any grounded conductor. If the SBJ is at the source, then you wouldn't have a second at the disconnect, and vice versa. In other words, you'd keep grounded and grounding conductors isolated at all but the location of the SBJ. As for the redundancy compared to a service transformer, I can only surmise the CMP has there own idea on what grounding is necessary.
250.30(A)(3) Grounding Electrode Conductor, Single Separately Derived System.
The grounding electrode conductor is required to be connected at the same point as SBJ. The buildings grounding electrode system is required to be bonded to the systems neutral at the same point as the SBJ bond to the system neutral.
How is that possible if a SBJ is required at the outside transformer and the SBJ cannot leave the enclosure where it is connected at, the buildings grounding electrode system is required to be bonded at the same point as the connection of the SBJ. You would have to have two system bonding jumpers one at the transformer and one at the MDP for the building.
In that case wouldn’t you size the neutral for threefold purpose? Insuring that it is sized no smaller than 250.66 and no smaller than 12 ? percent of the phase conductors and sized to carry the unbalance.
I really do not see the difference as a particle mater if a building is supplied by a utility transformer (service) or an SDS transformer. The supply to a buildings MDP from a n SDS is not a feeder.