I feel like this thread is become more of an ASSAULT than a useful discussion of any type,
I am sorry you feel this way. The question asked by the original poster did not get answered until the last couple of pages. It took some discussion before the object of the question got addressed.
Hello,
I'm working a job in Downtown Los Angeles area and the inspector hit me for not having a HOT water bond. I'm familar with inspectors calling for the gas to cold water, which I did at the water heater; then in a continious run, ran to the new 100 amp meter main service. I ran an additional bond straight to the new ground rod just below the panel. Doesn't the fact that the plumbing is tied together at the facets eliminate the need for a redundant bond to the hot water?
Thanks.
It has been only in the past few posts that the truth has come out that there is no verbiage in the NEC that this or any other inspector can use to enforce the bonding across a water heater.
The requirement found in 250.104 does not mandate that any metal water or gas pipe be made electrically continuous. The only requirement is that the point of connection be accessible. Bonding of the hot to cold pipes cannot be enforced by a code section therefore it is not required by the NEC.
Your jurisdiction can amend the NEC and require that the two be bonded but in order for this to happen it must be recorded somewhere in writing that can be produced. The idea of what most call the AHJ or what is in fact the inspector or code enforcement official cannot just decide that he wants to interpret the code to mean that there are two systems, one hot and one cold unless it is in writing that he can produce as the adopted code for that jurisdiction.