using your logic 0 Z is best, giving infinite i sc
the energy i^2 x t is proportional to time but the square of i
what z is best then? if not 0. all systems have a maximum short circuit current for a fault, its not infinite available current
it depends on what impedance and time your talking about. if the difference is the ocpd opening in 1 or 1/2 cycle instead of 30 it has a negative effect
obviously
but we talking on the order of
we are not talking about the same thing, your just talking about the ratio's of time and current compared to energy. if you play with formulas what you are saying is true but those ratios are relative. what matters is the real world affect of fault impedance
here's an extreme example
480/3, 80 A load, 100 cb, line-line fault
1% total v drop 4.8 v, z = 4.8/80 = 0.06 Ohm
5% total v drop 24 v, z = 24/80 = 0.30 Ohm
1% isc = 480/0.06 = 8000 A (80 x ir)
5% isc = 480/0.3 = 1600 A (16 x ir)
what is the trip time for each?
what is the i^2 r energy?
trip time is dependent on the ocpd your using, there all different
most meet standard approval agency guidelines, ul, iec, etc
they have to in order to protect standard conductor sizing/ampacity ratings
it's why you can't use a 100 cb with a #12 lol
just pick any off the shelf eaton cb
we are honestly talking about 2 different things. 1% and 5% impedance in real world is very big difference while 8ka and 1.5ka fault current is not
sure you can
fusing current for #12 copper is 235A
NEC 310.15(C)
310.15(B)(19)
#12 tfe good for 78A
my example is real world
for the same 100 A 480/3 1.6 ka vs 8 ka is a huge difference
1000 A ckt
1% z = 4.8/800 = 0.006 Ohm, isc = 80 ka (80 x ir)
5% z = 24/800 = 0.03 Ohm, isc = 16 ka (16 x ir)
both ~ instantaneous (>13/15 x ir)
is a factor of 5 or 64 ka a big difference?
go ahead, pick ANY cb
a 22kaic breaker
the system would already be properly designed the breaker would never see 80ka
REAL WORLD
a 22kaic breaker
REAL WORLD
do you commonly use breakers that go that high?
no system has infinite ampacity
Square D MAL361000