tlaidman
- Cleveland Ohio
while teaching box fill it was brought to our attention that the volumes listed in NEC 314.16 are less than if you do the calcs yourself. does anyone know why.
either!.....a normal square box say 4" x 1 1/4" you only use the 4" x 1 1/4" which would give you 18 cubic inch.....
websparky said:OK..... I think I see the problem!
The OP is asking why the table says 18cu. when the apparent size of the box is 4" x 4" x "1 1/4". The math on this is 4x4=16x1.25=20. The actual size of the interior of the nominal 4 square box is 3 13/16 x 3 13/16 x 1 1/8. The math is 3.815 x 3.815 = 14.55, x 1.125 = 18.19 or 18cu. just like the code book!
However, I still don't get either!![]()
a normal square box say 4" x 1 1/4" you only use the 4" x 1 1/4" which would give you 18 cubic inch because the table lists it as a square box.....
Cavie said:Since 20 in plastic boxes are not in the table 314.16(a), do we use table 314.16(b) and figure 2.25 in for each #12 and 5 in for each yoke?