Hello Guy's, I will be installing a crap load of Hand Dryers in a Commercial facility and need some help with the code requirements. The dryers are 208V, 6.6 amp each. I want to run 10 ga. on 30 amp DP GFCI breaker branch circuits so that I can cut down on the # of cable pulls, using 10/4 with Groung, Armored. Each dryer will be fused, using 15 amp glass fuses on each leg at the dryers on that circuit. I want to put 4 dryers/circuit. 2 circuits/cable. Must I run 10 gauge to each dryer from the Home run connection box? Or can I run #12 from the splitter box to the dryers? Since they are all individually fused. Thanks for any help. I am pretty sure I must run 10 wire throughout though.