If there were a 5A or 10A breaker, it likely would have the same physical construction as a 15A breaker, with just a different trip calibration. Usually, the DIN rail breakers that would exist in 5A or 10A sizes, are built in sizes up to 30A, and all breakers in any given family, are 90% the same with just the trip mechanism being different.
Understood.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Except for SABCs, bathroom receptacles, laundry and some other dedicated circuits, you could put the entire rest of the house on one 15A circuit if you wanted.

-Hal
Only if the house was 600 square feet or less. 210.11(B) requires that you install the number of 15 or 20 amp branch circuits based on the general lighting and receptacle load at 3 va per square foot.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Where do you see that? This is from the 2023.

(B) Load Evenly Proportioned Among Branch Circuits. Where
the load is calculated on the basis of volt-amperes per square
meter or per square foot, the wiring system up to and including
the branch-circuit panelboard(s) shall be provided to serve not
less than the calculated load. This load shall be evenly proportioned
among multioutlet branch circuits within the panelboard(s).
Branch-circuit over current devices and circuits shall
be required to be installed only to serve the connected load.

-Hal
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Where do you see that? This is from the 2023.

(B) Load Evenly Proportioned Among Branch Circuits. Where
the load is calculated on the basis of volt-amperes per square
meter or per square foot, the wiring system up to and including
the branch-circuit panelboard(s) shall be provided to serve not
less than the calculated load. This load shall be evenly proportioned
among multioutlet branch circuits within the panelboard(s).

Branch-circuit over current devices and circuits shall
be required to be installed only to serve the connected load.

-Hal
right there
 

garbo

Senior Member
Never made sense why they never made single pole circuit breakers to match size of Edison base screw in fuses. Often came across a red little single pole safety switch that supplied power to fire bells in triplex and small apartment units that had a 3 amp fuse. All the wiring was in type AC cable. My moms old house still has a gravity feed natural gas heater that the 15 amp circuit breaker only feeds a maybe 50 VA 120 to 24 volt transformer that draws less then 0.5 amps and would rather have a 3 amp circuit breaker protecting it.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
My moms old house still has a gravity feed natural gas heater that the 15 amp circuit breaker only feeds a maybe 50 VA 120 to 24 volt transformer that draws less then 0.5 amps and would rather have a 3 amp circuit breaker protecting it.
Primary side OCPD are not intended to protect the transformer, although they might. Their real purpose is to remove a faulted transformer before it causes issues with the premises wiring.
Small transformers, like for furnace and door bells, are usually impedance protected against excessive current on the secondaries.
 
Last edited:

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Never made sense why they never made single pole circuit breakers to match size of Edison base screw in fuses.
1714138797284.jpeg 1714138813470.jpeg


 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Ok. I calculated that one 15A circuit is sufficient to supply the general purpose receptacle and lighting loads of a 1200 sq ft house.

(A) Number of Branch Circuits. The minimum number of
branch circuits shall be determined from the total calculated
load and the size or rating of the circuits used. In all installations,
me number of circuits shall be sufficient to supply the
load served. In no case shall the load on any circuit exceed the
maximum specified by 220.1 .

-Hal
 

BarryO

Senior Member
Location
Bend, OR
Occupation
Electrical engineer (retired)
So given that fact, when someone goes to get their NRTL (UL, ETL, CSA) listing of a DEVICE that is small enough to be used on a 15A branch circuit, the listing of that device has to take into account that the BCPD protecting it will be 15A.
A nit, but the device has to take into account that the BCPD protecting it will be 15A or 20A, since 20A branch circuits may have NEMA 5-15 receptacles on them.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Ok. I calculated that one 15A circuit is sufficient to supply the general purpose receptacle and lighting loads of a 1200 sq ft house.

(A) Number of Branch Circuits. The minimum number of
branch circuits shall be determined from the total calculated
load and the size or rating of the circuits used. In all installations,
me number of circuits shall be sufficient to supply the
load served. In no case shall the load on any circuit exceed the
maximum specified by 220.1 .

-Hal
Is that a multi-wire branch circuit?
 

Grouch1980

Senior Member
Location
New York, NY
So, from what I gathered from this thread, is the following:
1. For small loads, such as a 2.6 amp air handler with a 15 amp breaker, it's not the job of the circuit breaker (or fuses) to protect the load. The breaker or fuses only protect the wiring to the load. The manufacturer has to design their equipment appropriately, so that there's no spontaneous overloads. Or in the case of something like christmas lights, the load can sometimes come with its own internal / secondary protection.
2. For larger loads, say a 50 amp heater, the manufacturer may now rely on the circuit breaker for protection, unless they design their equipment appropriately as I mentioned above.

Do I have it right?
 
I think sometimes the serving OCPD is taken into account when designing the equipment, but it nothing you have to worry about. Equipment typically has to meet some listing or product standard, and I am not familiar with those requirements and the testing process, but I imagine the serving OCPD is considered. A few examples are HVAC units that have a max fuse or breaker size. Another is transfer switches where the SCCR will depend on the OCPD. The manufacturer provides a list of different OCPD 's and the resulting allowed SCCR.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
To add electrofelon's last reply, in my experience if it is a hardwired appliance it will almost always say something about the max OCPD in the instructions. If it is a plug-in load then I believe the design and listing process assumes that the receptacle will be properly wired according to the code, and thus certain assumptions are made based on the type of plug used. That is, I agree that as long as instructions are followed you don't need to worry if the OCPD is larger than the load. The OCPD rating always needs to be larger than the expected load anyway to avoid nuisance trips.

Also, one thing to add is that 10 amps is a standard breaker size and the manufacturers do make them. Harder to find (probably buy online or special order if going through a supply house) but they exist.
 
Last edited:

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I have seen some talk on the forum about the code possibly allowing 10 amp lighting circuits with 16awg in the future, but that hasn't happened yet. With mostly LED bulbs all the lighting in my house wouldn't draw 10 amps.
 