Unless this is a regularly washed down area, EMT will probably last much longer then it would if it were outdoors.
I came into the trade a fairly long time ago. Pvc electrical conduit was invented and in use, but not for very long at that point. Some local area's near where I worked were not allowing it to be used yet. At my first place of employment they would paint lap seal on emt and bury it direct in the soil. I doubt any of those installs made it this far, and are completely rusted away to powder by now.
1984, hotel meridian across from john wayne airport. {Edited to remove the name of the electrical contractor said to be responsible for the installation described below.}
1/2" emt home runs, they'd run 100'+ in a post tension slab,
and then turn down with a red dot 90 above where the panel
would go. they'd turn up wherever, in emt. no GRC where it
would exit the pour. concrete listed fittings. no duct tape.
the concrete paddle machines would grab them during finishing,
and twist them off, leaving the stub looking like the twisted end
of a cigarette that i'm sure the general foreman who thought all
this up was smoking.
3/4" emt home runs, 100' plus, stubbing up into a riser that went
up six floors, feeding that plug in every room. 3/4" emt in the bottom
of the box, 3/4" emt out the top of the box, a 1/2" out the side of the
box to feed a plug down the wall, full house in the bottom, full house
out the top, and a device in the box.... and it's a 104 box.
why no, i'm not a big fan of emt in the slab...... i spent the first two
months working there fixing broken 1/2" emt stubs, and found one
that was tie wired to a post tension cable, that i nicked one day
while dissecting around the emt, not realizing that it was a post tension
cable until it became less tense, all of a sudden.
they make a loud bang, by the way.
As dumb as it sounds, set screw , steel fittings say suitable for concrete. I have , nor will I ever try this. All it takes is one bad joint, ie: tape joint and bam, a lost raceway. II have seen EMT fitting that stated they were listed for use in concrete if they were wrapped in duct tape. It was a long time ago, and I honestly can't remember the name of the manufacturer, but I kind of laughed when I read it.
Yes it is, for all the safety and preventive we do, and all the NEC provides for us to follow. Running EMT in concrete, or dirt makes little sense. Especially if you have ever seen what happens in a hotel to the raceways after several years of prolonged use. Not much common sense in that coding for sure. But as Mike Holt says " for test purposes the answer is 358.10(b). LolWhat about column 3, other approved raceways?
And yes it can be buried. Says so in 358.10(B)
(B) Corrosion Protection.
Ferrous or nonferrous EMT, elbows, couplings, and fittings shall be permitted to be in-
stalled in concrete, in direct contact with the earth, or in
areas subject to severe corrosive influences where protected
by corrosion protection and approved as suitable for the
condition.
Horrible idea though.
As dumb as it sounds, set screw , steel fittings say suitable for concrete. I have , nor will I ever try this. All it takes is one bad joint, ie: tape joint and bam, a lost raceway. I
Sent from my XT1254 using Tapatalk
Though I agree, I don't believe NEC should take the position that PVC is all that is allowed to be embedded in concrete, that is a design decision.The real question is why?
PVC faster, easier, cheaper.
I don't believe NEC should take the position that PVC is all that is allowed to be embedded in concrete, that is a design decision.
Over the past year I've dealt with several 1960's era buildings that were wired with RMC in the slab, and of course TW or RHW wire in them. Long story short, the conduits were rotting out and shorting, so we ended up having to refeed over head which is no easy task. We all know there is little to no chance of pulling rubber and cloth conductor out of rotted conduit. Obviously, PVC was not in use in the 1960's but given that metal raceways can have a short life in adverse soil conditions where PVC does not, PVC is the obvious choice to me.