I'm glad you see now that 250.118(8) doesn't apply to ex-AC cable.
Read it carefully, five words, no qualifications in the words:
2014 NEC 250.118
(8) Armor of Type AC cable as provided in 320.108.
Come on Wayne, you're better than that. You meant to actually QUOTE the Code, I'm sure, not misquote it.its armor does not meet the construction specification of 320.108.
2014 NEC 320.108 Equipment Grounding Conductor. Type AC cable shall provide an adequate path for fault current as required by 250.4(A)(5) or (B)(4) to act as an equipment grounding conductor.