As I have said, I'm offering Code. I have also said I am not an expert. I have been learning a lot in the course of this thread. I have been put in mind of Charlie's Rule and been buoyed by the experience in the area I work in.Again Al you are entitled to your opinion but many of us do not agree with it and that does not mean we are misquoting anything.
Just as you are entitled to your opinion we are entitled to ours.
The term "EGC" or Grounding Conductor, Equipment was first in Article 100 Definitions in the 1968 NEC. It was split out of the earlier Article 100 Definitions term "Grounding Conductor".So, this thread has inspired me to put the physics aside and view it from purely a code perspective. I must ask, the older NECs, is BX mentioned anywhere as an EGC?
The term "EGC" or Grounding Conductor, Equipment was first in Article 100 Definitions in the 1968 NEC. It was split out of the earlier Article 100 Definitions term "Grounding Conductor".
So, this thread has inspired me to put the physics aside and view it from purely a code perspective. I must ask, the older NECs, is BX mentioned anywhere as an EGC?
Also, to work towards better clarity, "BX" isn't mentioned at all in the NEC. Only Armored Cable type AC.
No, when the definition of type AC cable changed in 1959, or thereabout, it ceased to be AC cable.Old non bonding strip Armored Cable, in 1937 and on, IS type AC.
In the pre 1968 NEC, the term is "GC" or Grounding Conductor. Yes. I've shown that all the way back to the 1918 NEC in this postAnd AC can be used as an EGC in these older NECs?
250.118(8) doesn't specify what you claim.No, when the definition of type AC cable changed in 1959, or thereabout, it ceased to be AC cable.
Great. Old ex-AC cable has a (pre-1968) GC.In the pre 1968 NEC, the term is "GC" or Grounding Conductor. Yes. I've shown that all the way back to the 1918 NEC
Sure it does:250.118(8) doesn't specify what you claim.
a) 320.108 is a construction specification.
Are you claiming that ex-AC cable actually meets those requirements?
That tells me that if it is type AC cable, and its armor meets the provisions of 320.108, then it is an EGC.2011 NEC said:250.118(8) Armor of Type AC cable as provided in 320.108.