peter d
Senior Member
- Location
- New England
You have been shown by a number of folks you just don't agree with it and that is fine.
I think it's fine as long as everyone else understands that Al's position is wrong.
You have been shown by a number of folks you just don't agree with it and that is fine.
You have been shown by a number of folks you just don't agree with it and that is fine.
I have carefully read and participated in this thread with honesty and candor for which I have been called a sophist and been otherwise challenged as to motive.
To claim that 2014 NEC 250.118 reverses Armored Cable type BX installed as a grounding means status as of the 1959 NEC has ramifications for other legally installed grounded wiring. This claim, when told to clients who have BX is, in my opinion, illegally manipulating them.
If the client is told only of the safety hazards, good.
But not by misquoting the Code.
Look,I think it's fine as long as everyone else understands that Al's position is wrong.
Look,
I agree BX is not a good ground. But to say the new code requires that you replace the BX just because you maintained a receptacle is baffling me. By that same logic, if I maintain a receptacle on a circuit without an AFCI breaker then I now have to change the breaker. That is crazy.
What did I miss?
Look,
I agree BX is not a good ground. But to say the new code requires that you replace the BX just because you maintained a receptacle is baffling me. By that same logic, if I maintain a receptacle on a circuit without an AFCI breaker then I now have to change the breaker. That is crazy.
What did I miss?
You are overstating the argument that has been made (although some may have made it). It is only necessary that the replacement receptacle, if it has a ground connection which the original receptacle did not, follow the rules for adding a three wire receptacle to a groundless circuit.Look,
I agree BX is not a good ground. But to say the new code requires that you replace the BX just because you maintained a receptacle is baffling me. By that same logic, if I maintain a receptacle on a circuit without an AFCI breaker then I now have to change the breaker. That is crazy.
What did I miss?
250.118 does. And before you say that your "code path" doesn't get you there, you got there in post 199. In that you got to the definition of EGC, which directs you to 250.118.My position is that nothing in the Code, in the current edition or in "superseded" editions has removed the status of "existing grounding means" by direct rule.
You are overstating the argument that has been made (although some may have made it). It is only necessary that the replacement receptacle, if it has a ground connection which the original receptacle did not, follow the rules for adding a three wire receptacle to a groundless circuit.
IMHO adding an explicit ground connection as part of a circuit which did not previously offer that connection is an extension. It is not a one-for-one device replacement.
Look,
I agree BX is not a good ground. But to say the new code requires that you replace the BX just because you maintained a receptacle is baffling me. By that same logic, if I maintain a receptacle on a circuit without an AFCI breaker then I now have to change the breaker. That is crazy.
What did I miss?
According to people on this site you DO have to change the breaker if you replace a receptacle on a circuit that should be AFCI.
That's crazy! That's absurd! That's found in 406.4(D)(4)!
(D) Replacements. Replacement of receptacles shall com-
ply with 406.4(D)(1) through (D)(6), as applicable. Arc-
fault circuit-interrupter type and ground-fault circuit-
interrupter· type receptacles shall be installed in a readily
accessible location.
Exception: Where replacement of the receptacle type is
impracticable, such as where the outlet box size will not
permit the installation of the GFCI receptacle, the recep-
tacle shall be permitted to be replaced with a new recep-
tacle of the existing type, where GFCI protection is pro-
vided and the receptacle is marked "GFCI protected" and
"no equipment ground," in accordance with 406.4(D)(2)
(a)j . (b),or( c).
That is clearer to me.Where did I ever claim the BX had to be replaced? I only said it has to be replaced if you want a modern, grounded system with grounded receptacles. If it's existing, it cannot be used for grounded receptacles if and when the time comes to replace receptacles.
Al's belief is that he can install a new, grounded receptacle as a replacement and use the BX armor as a suitable EGC. His reasoning and logic is that the system was considered grounded from the beginning, so it can stay that way. I have maintained all along that his position is wrong based on the fact that the NEC does not recognize unbonded BX armor as an EGC and any modification to an existing system, including receptacle replacement, has to follow the current code.
Truthfully, I don't get what was unclear about anything I have said.
Which is what I would do unless they wanted to pay for a re-wire (the bank in the OP did not).I don't think anybody here has posted that the only option is to gut the old stuff- rather we have mentioned rep 2 wire recs as well the gfci feeding 3 wire outlets allowance as good viable alternatives to rewiring.
You could argue tha connection was previously offered through the spade terminal to screw but I don't remember the years and if they overlapped the BX ground years.IMHO adding an explicit ground connection as part of a circuit which did not previously offer that connection is an extension. It is not a one-for-one device replacement.
Iwire said he would not go the GFCI route.
Let me clarify that, I would not install 3 wire receptacles on a BX circuit with or without a GFCI.
I do still have old BX in my home and don't live in fear of it burning down the house.
So Al thinks there is a "loophole" so to speak via code interpretation. .
My question is would a GFCI fault trip on a BX circuit before there was enough current flowing through the armor to present a problem?