Still, the problem is the type you depict is not a listed cable, and more importantly, not recognized as a cable under the NEC. Even though the manufacturer calls it twisted cable, under the NEC it's just twisted XHHW-2 conductors.
Now if you go with the USE-2 version, it is UL 854 listed as Service-Entrance Cable and a recognized cable under the NEC. See page linked below and spec' sheets for each type.
http://www.servicewire.com/serviceplex-v2.php
Have you read UL-83 and 44 as well in regards to multiconductor cable?