Just need a sanity check to make sure the following statements are true:
· TC-ER control cable (non-shielded) terminates in factory-sealed 'Start-Stop' PB station –
No cable seal required based on 501.15(E)(1) and 501.15(E)(3), i.e. may use C-H, CGB, TMC or equal fitting for termination.
· MC-HL control cable (non-shielded) terminates in NON-Factory-sealed 'Start-Stop' PB station – Cable seal required based on501.15(E)(1) and 501.15(E)(2), i.e. must use C-H, TMCX or equal fitting for termination.
LNG plant, Class I, Division 2 Gps C&D
· TC-ER control cable (non-shielded) terminates in factory-sealed 'Start-Stop' PB station –
No cable seal required based on 501.15(E)(1) and 501.15(E)(3), i.e. may use C-H, CGB, TMC or equal fitting for termination.
· MC-HL control cable (non-shielded) terminates in NON-Factory-sealed 'Start-Stop' PB station – Cable seal required based on501.15(E)(1) and 501.15(E)(2), i.e. must use C-H, TMCX or equal fitting for termination.
LNG plant, Class I, Division 2 Gps C&D