Boys, quit your bickering, you've made your points. I relocated your posts, they were derailing the thread.
I had forgotten about this thread until someone revived it.
After the second visit, all was well for over a month. Then I get a call saying they lost power to the room again.
I went back and of course when I get there everything is working. But I wasn't about to leave without checking things out. I loaded up the circuit and went to the panel to check the voltage and current. The breaker tripped and my meter showed around 18A. The breaker was only a 15A so I thought they were just overloading it. So I decided to swap the breaker out to a 20A since they already had #12 wire run.
I still felt uneasy and didn't want to come back to this again so I decided to just dig into this as deep as I could.
First of all, you would need to know I was getting conflicting info between the HO (lady) and her son. The lady originally told me 1/2 the room was out and that's when I found the two bad 3-way switches. When she called the second time she said it was all out and that's when I found the loose neutrals and replaced the breaker which looked a little suspect due to corrosion on the screw/lug, but looked ok on the stab.
The son wasn't sure if everything was out or just 1/2 the room. So I just put their info aside and checked the panel and found several loose neutrals. Tightened them all up, ran everything for a while, then left.
Ok, back to the update. After replacing the 15A breaker with the 20A, I took the hot off the breaker and traced it up to where it entered the panel so I could see which neutral wire went with it. As I said I found several loose neutrals before and wanted to see if this was one of them. I thought I had found the right neutral before, but apparently didn't because of the way they were twisted and crossing each other.
When I traced the neutral down I found it had been hot and the insulation had melted and fused to two other neutrals that were close to it. So I cut off the burnt neutral above where it was burnt, spliced on a new piece of wire and relocated it on the bar.
Turns out the threads of the screw on the neutral bar had welded it's self to the hole, making it appear tight when checking with a screwdriver. But although the screw was tight, it wasn't all the way against the wire making a loose connection. IMO, that's what caused it to overheat and melt the insulation off.
This was about 2 weeks ago and all seems well now.
It was just odd that I found more than one problem that could have caused the loss of power.
should I have charged for the second trip?
You unplug everything in the house, then check a second time. This requires moving just about everything in the house to be sure. Then you remove all light bulbs including attic and crawlspace and the ones outside in the fixtures that need to be opened up, some of which need a ladder to get too. Remove and disconnect every GFCI, including the ones outside of the house in outdoor boxes/covers. Remove and disconnect smoke detectors. Disconnect the furnace. Remove and disconnect motion detection lights. Remove and disconnect every dimmer. Disconnect the door bell transformer. And probably a few other things that I am forgetting.
You do all of that, and THEN you do all the work of actually doing the meggering, and also find the fault- all in 20 minutes, everyday?
I am not going to claim it can be done in 20 minutes, but one suggestion is once you have unplugged things removed lamps, etc. to test the circuit with meter in low resistance range before megging. If you have anything but an infinity reading you likely still have something connected to the circuit.
But this testing only tests the premises wiring, you have to remember that unplugged equipment could contain problems also, so just megging things and telling the customer everything is fine will result in callbacks when they plug the defective equipment back in.
After you measure for drops and you have your megger connected you can plug a plug tester in and lightly shake each outlet when you find a loose connection the megger will jump when you shake it.