- Location
- Massachusetts
If I am reading this right the 240 volt 50 amp outlet should be calculated at 9600 VA. The 120 volt 30 amp outlet with a 20 amp GFCI outlet should be calculated at 3600 VA.
9600 VA + 3600 VA = 13200 VA
13200 VA ÷ 240 volts = 55 amps
55 amps × 1.25 = 69 amps
80 amp feed breaker
Two #4 THHN hots
One #6 THHN neutral
One #8 THHN ground
In my opinion adding the 125% is not required and no need to round up 11 amps but it is certainly code compliant.
You could do a 60 amp with 6 AWG not factoring voltage drop.