hurk27
- Portage, Indiana NEC: 2008
The 6 amps there abouts @ 50 volts would give you about 8.3 ohms of the whole circuit Including the wiring, at 120 volts this would provide about 14.5 amps, but one thing I am confused with is the variable 0-120 volt section you have the banana plug in to states @ 5 amps? I have worked with a few lab power supply's and the OCPD has current coils with different ratings for each section IE. 15 amps for the non-variable 120/208, and 5 amps for the variable 0-120/0-208, 8 amps for the non variable 0-120 DC and 2 amps for the variable 0-120 DC, this is so only one reset is required.
I'm not so sure you actually ever reached 120 volts before the OCPD tripped?