I do not believe there are any specific bonding requirements to meet. Consider the hinged cover of a disconnect switch.
:grin:
How about this, now you can compare it's size against a Fluke T5 tester.
![]()
So is the screw or cover a switch, circuit breaker, or overcurrent device?iwire,
I think it is wrong to use those screws. Yes, they'll do in a pinch, but I'm still going with 250.8(5), (6), and(7) because if we look at 408.2, Art 314 is included. 314.40 (B) goes over thickness of the metal:
What has grounding and bonding got to do with it?and two of the threads of the shown screws are greater in depth than that of the thickness of the metal, and so ideally(sp?) there is not 2 threads engaged.
Sheet metal screws are for sheet metal
Oooooooh. That waskaly wabbit.So you agree I can use sheetmetal screws. :grin:
Panel cabinets and panel covers are sheetmetal.
(Generally flat metal thinner than than 1/4" is considered sheet metal, 1/4" and thicker is steel plate)
Oooooooh. That waskaly wabbit.
INSTALLING THE COVER
1. Remove the cover twistouts.
a. Remove only enough twistouts to match the number of circuit
breakers being installed.
b.Twist out with pliers at the center of the twistout. See Figure 8.
c.Close all unused open spaces in the cover using filler plates
as listed on the cover directory label.
2. Attach the Spanish translation label, if supplied with the load
center, to the rear of the cover. See Figure 9.
3. Identify the branch circuits on the directory label.
4. If the load center is used as service equipment, apply the
“Service Disconnect” label to the part of the cover nearest the
main circuit breaker handle. If the load center is not used as
service equipment, apply the “Main” label to the part of the cover
nearest the main circuit breaker handle.
5. Install the cover using the screws provided.
A little digging and I found a typical SquareD Panel Installation Guide...
http://ecatalog.squared.com/pubs/Electrical%20Distribution/Load%20Centers/Homeline%20Single%20Phase%20Load%20Centers/40271-419-04.pdf
On page 4 of that instruction:
Here are some spare parts you can carry...
http://ecatalog.squared.com/pubs/Electrical%20Distribution/Load%20Centers/Accessories,%20QO%20(LK,%20PK,%20QO,%20QON)/1130DB0502.pdf
Now, if you lost the screws or they were not in the package, I guess there would be a bit of a problem...![]()
BTW, not all panel covers use machine screws.
Some have specialty threads. Look close. Some have two threads so the taper is different than with a single thread of the same cut.
I guess my question is why the manufacturer would go to such extent to make a double threaded screw and then allow a sheet metal screw to be used in it's place? To me, such a substitution would constitute a modification.
Do the panels still maintain their UL status if modified with an unapproved means?
A) Because someone in the design department had too much time on their hands...I guess my question is why the manufacturer would go to such extent to make a double threaded screw...
I bet Iwire was expecting me, of all people, to absolutely go *bonkers* over this poll....**
**I took some powerful medication to calm myself down enough just to write this post...:roll:
It should be noted at this juncture, that Bob has accepted large sums of money from the makers of Pepcid AC.