I have a 120VAC control circuit using a Magnecraft W388ACPSRX-30 Time Delay Drop Out Timer.
The 120VAC signal wire is between 30 & 60 feet long. It is routed in wire bundles that are about 2 to 3 inches in diameter.
When the contact opens to de-energize the timer a pesky 10 volts AC remains across the coil. This is enough to keep it latched. :-?
I am measuring the 10 volts with a Fluke 27. If I insert my SV225 to convert the meter to a low impedance input the relay drops out when my probes touch the terminals of the coil.
I can also place a 25K ohm resistor across the coil to make it behave. This is about 10 times the resistance of the SV225.
Is capacitive coupling a possibility ? I cannot find mis-wiring.
The relay uses 2W max @ 120VAC
The Fluke measures the coil resistance at 10M ohms.
Thanks in advance for any help.