crossman said:That's strange! My 2005 NEC says you can!
raider1 said:So does mine.
Ditto, it also says 'at least 20' of one or more bars.'
crossman said:That's strange! My 2005 NEC says you can!
raider1 said:So does mine.
ryan_618 said:So Bob, what if I drive a ten foot ground rod eight feet deep, then conect to the exposed portion of it? Are you saying that it is not an electrode because the electrode is only the part that is in the dirt? It seems like the same logic as your CEE argument...
iwire said:Ditto, it also says 'at least 20' of one or more bars.'
raider1 said:So does mine.
The last sentence of 250.52(A)(3) states:
"Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means."
Chris
So, in other words, a ground rod laying on the sidewalk is an electrode, because nothing in 250.52 says it has to be in the dirt? I think you must use both subsections...250.52 and 250.53 to determine what an electrode is. If I have an electrode that is permissable (an 8 foot rod) and I make it longer (a 10 foot rod) I can still connect to it in the above ground portion. If I take an electrode such as a piece of rebar that complies, I can also tie onto it wherever I would like.iwire said:IMO not the same.
250.52(3) describes a CEE as 'being encased in concrete'
250.52(4) does not describe a ground rod as being in the earth.
We don't get to the 8' earth requirement until we get to 250.53(G)
No length limitation. Can I tie to it with more tie wire...yes.Now can I ask you, how long can the sub be and can I splice onto to it with more rebar and tie wire? :smile:
tryinghard said:This does not say electrode.
ryan_618 said:So, in other words, a ground rod laying on the sidewalk is an electrode, because nothing in 250.52 says it has to be in the dirt?
think you must use both subsections...250.52 and 250.53 to determine what an electrode is.
If I have an electrode that is permissable (an 8 foot rod) and I make it longer (a 10 foot rod) I can still connect to it in the above ground portion.
If I take an electrode such as a piece of rebar that complies, I can also tie onto it wherever I would like.
No length limitation. Can I tie to it with more tie wire...yes.
Marc said:Seems like lately the upturned rebar is at the furtherest place in the basement from my panel location, so they're paying dear for that oversight.
ryan_618 said:What I am trying to get at is that simply making an electrode longer does not mean you must connect to the portion spelled out in .52 or .53.
ryan_618 said:Is the steel bar not an electrode? That is what is being described in the rest of the subsection.
iwire said:tryinghard, I don't know what else to say other then IMO your mistaken.
Read it using Charlie's rules, in my opinion your reading it with a destination in mind.
tryinghard said:I think the opposite of my argument is disgusting, to allow an undefined amount of chunks of steel to wire tie in some method of becoming an acceptable 20? electrode, all this done by crafts who have zero association of what the electrode is or why they are installing it.
iwire said:But a GEC must connect to 'the electrode', the part outside the pour is not the electrode.
e57 said:5' of a water line is still an electrode when not buried if 10' of it is,
and so would 2' of a 10' rod.
What if say you had a single 50' stick of re-bar and it were exotherically welded to the neutral bar of the main panel (2')- for the sake of conversation - then it went into the concrete floor below the panel and directly to 2" at the bottom of the pour (2') - travelled 10', then up to 5" in the pour for 5', then back down to 2" for another 10' - then did it again - up for 5', down for 10'. then stuck up and had the water clamped directly to it.... Is any portion of this single rebar an electrode?
So if all 50' were 2" from the bottom of the pour - where do you connect to it? In the middle - at the end - which end?
Like mentioned in my 'accessibility' argument - if the encased connection is actually an exception - how could one ever do a CEE without using the exception?
(And do my best to steer Inspectors clear of Bob)
tryinghard said:250.52(A)(3) does not say the CEE electrode can be wire tied to equal 20'!
250.52(A)(3) does say a CEE electrode consists of at least 20'.
cschmid said:250.52 Grounding Electrodes.
(3) Concrete-Encased Electrode.
An electrode encased by at least 50 mm (2 in.) of concrete, located horizontally near the bottom or vertically, and within that portion of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (1/2 in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG. Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means. Where multiple concrete-encased electrodes are present at a building or structure, it shall be permissible to bond only one into the grounding electrode system.
Ok I follow that..But I do not follow the exposed area of thought..As the connection to the CEE is not in violation according to 250.64 (f)(1) so does that mean having the rebar exsposed makes a convient location..
250.64 Grounding Electrode Conductor Installation.
(B) Securing and Protection Against Physical Damage. Where exposed, a grounding electrode conductor or its enclosure shall be securely fastened to the surface on which it is carried. A 4 AWG or larger copper or aluminum grounding electrode conductor shall be protected where exposed to physical damage. A 6 AWG grounding electrode conductor that is free from exposure to physical damage shall be permitted to be run along the surface of the building construction without metal covering or protection where it is securely fastened to the construction; otherwise, it shall be in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, electrical metallic tubing, or cable armor. Grounding electrode conductors smaller than 6 AWG shall be in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, electrical metallic tubing, or cable armor.
(F) Installation to Electrode(s). Grounding electrode conductor(s) and bonding jumpers interconnecting grounding electrodes shall be installed in accordance with (1), (2), or (3). The grounding electrode conductor shall be sized for the largest grounding electrode conductor required among all the electrodes connected to it.
(1) The grounding electrode conductor shall be permitted to be run to any convenient grounding electrode available in the grounding electrode system where the other electrode(s), if any, are connected by bonding jumpers per 250.53(C).
cschmid said:So my question is does the re-bar in 2 inches of concrete that is elevated of the ground still qualify as CEE as the concrete is not in direct contact with the earth..And does it actually have the same grounding resistance as it would being in direct contact with the earth...
iwire said:So a re-bar stubbed out of the footing is just re-bar not a CEE. :smile:
250.68 Grounding Electrode Conductor and Bonding Jumper Connection to Grounding Electrodes.
(A) Accessibility. The connection of a grounding electrode conductor or bonding jumper to a grounding electrode shall be accessible.
It used to say the whole water line was - it only changed due to changes in Plumbing practice...Quote:
Originally Posted by e57
5' of a water line is still an electrode when not buried if 10' of it is,
It is because the NEC says it is.
Quote:
and so would 2' of a 10' rod.
It is because both the NEC and UL says it is.
The upper end of the electrode shall be flush with or below ground level unless the aboveground end and the grounding electrode conductor attachment are protected against physical damage as specified in 250.10.