electrofelon
 - Cherry Valley NY, Seattle, WA
 - Electrician
Yes I use those frequently
I know. I was suggesting an alternative that should satisfy bonding and spacing concerns.this is more what i was thinking of for a chase nipple:
Now that, I would use as a bonding connector. That is if I used a bonding connector when I could use a bonding wire instead... It's an industrial thing.
I’ll often see people use these indoors on transformers or panels entering in with an LB and using these instead of a close nipple with lock rings.this is more what i was thinking of for a chase nipple:
I use box adapters that way often but it's pvc then so no issues with bonding everI’ll often see people on use these indoors on transformers or panels with an LB instead of nipple and lock ring.
Not sure if they are allowed to be used like that![]()
I try to avoid using garbage die cast fitting into & lock nuts especially outdoors. Had way too many die cast lock nuts split after not even going crazy tightening them. NEC should just mandate that a wire must always be used for grounding verses long term unreliable use of conduit or armored cable. Have came across too many rusted thru conduits, broken pieces of sealtite and EMT that were pulled out of fittings all creating a dangerous non grounded condition due to no ground wire was installed. While I'm on a rant wish the NEC would outlaw AC cable. In my area for last 35 years you must use far superior type MC cable in commercial sites rather then AC cable.
Try saying this to a industrial planner who does rmc everything and they'll look at you as a little silly. Often those use conduit bodies for splices that don't even have a spot for ground screws.I try to avoid using garbage die cast fitting into & lock nuts especially outdoors. Had way too many die cast lock nuts split after not even going crazy tightening them. NEC should just mandate that a wire must always be used for grounding verses long term unreliable use of conduit or armored cable. Have came across too many rusted thru conduits, broken pieces of sealtite and EMT that were pulled out of fittings all creating a dangerous non grounded condition due to no ground wire was installed. While I'm on a rant wish the NEC would outlaw AC cable. In my area for last 35 years you must use far superior type MC cable in commercial sites rather then AC cable.
Many, including me, will vehemently disagree with you here. In a recent thread in fact I was complaining that AC cable should be more common over MC. I do think minimum fitting quality needs to be a bit higher and/or enforced.I try to avoid using garbage die cast fitting into & lock nuts especially outdoors. Had way too many die cast lock nuts split after not even going crazy tightening them. NEC should just mandate that a wire must always be used for grounding verses long term unreliable use of conduit or armored cable. Have came across too many rusted thru conduits, broken pieces of sealtite and EMT that were pulled out of fittings all creating a dangerous non grounded condition due to no ground wire was installed. While I'm on a rant wish the NEC would outlaw AC cable. In my area for last 35 years you must use far superior type MC cable in commercial sites rather then AC cable.
I believe that threads on chase nipples are never tapered like threads on rigid heavy wall conduit. That's why a locknuts usually will easily spin to neck of chase nipples but not on rigid conduit. Maybe 7 or 8 years ago at a continuing education class was told you should never screw a chase nipple into a heavy wall coupling. And yes I have screwed 1/2 to 2" chase nipples thru a box or pecker head into a heavy wall coupling made up wrench tight and they never came loose but always pulled a ground wire.inspector said " prove a tapered shoulder of a chase nipple is UL listed for grounding"
This is what I have
1663.pdf
I am locked out of my Iq for UL looks like 514b address this issue from what I can gather online, but most spots I go want me to buy the book.
Thanks for this great picture. I checked threads on several 1/2 & 3/4" T & B insulated & regular chase nipples and steel locknuts spin easily up to hex shoulder making me to believe they do not have tapered threads. Will have to dust off my micrometer and see if I can find a difference .I saw this on a box the other day. Manufacturer instructions seem to contradict UL listing regarding threads.
EMT connector is bonding a single enclosure (possibly with the locknut penetrating through painted finish) to the fitting then to the raceway. Same thing occurs at other end of raceway when you hit another enclosure.Me too. I see no issue. No different than an EMT connector into a box.
If you look closely at the photo it tells you the thread type, NPSM.Thanks for this great picture. I checked threads on several 1/2 & 3/4" T & B insulated & regular chase nipples and steel locknuts spin easily up to hex shoulder making me to believe they do not have tapered threads. Will have to dust off my micrometer and see if I can find a difference .
Did a Google search and it stated NPSM ( or American Standard Straight Mechanical Pipe Thread ) and they do not have a taper pipe thread. Type NPS stands for National Pipe Thread and have a tapered thread. When I started as an apprentice our electric shop had an old set of 1/2 to 2" Rigid stock & dies that only the sparkies were supposed to use. A know it all plumber asked to borrow them and I tried to explain that I was told they were not for use on plumbing pipe. Of course he told me that I was another dumb rookie. He threaded at least halve a dozen pieces of schedule 40 pipe for a 125# steam line. He spent hours taking first leaking joint and applying more pipe dope, put it together then tried fixing next leak. End of day somebody in our shop that heard our conversation told him he used the wrong dies. These dies did not produce a tapered thread and hopefully no longer produced. Came across European 2 to 5 KW immersion heaters that had straight threads. Some how it was the electricians job to remove bad heaters & wrench in new ones. Luckily we had a very talented chief electrician and he finally told us how to stop threads from leaking water. After we applied several layers of Teflon pipe tape wrapped two pieces of sewing threads onto taped threads. These heaters were on melting kettles and little pump only produced 10# of water pressure.I saw this on a box the other day. Manufacturer instructions seem to contradict UL listing regarding threads.
And yes. Plumbing dies and electrical dies are different. NPS is straight and NPT is tapered.
344.28 Reaming and Threading. All cut ends shall be reamed or otherwise finished to remove rough edges. Where conduit is
threaded in the field, a standard cutting die with a 1 in 16 taper (3∕4 in. taper per foot) shall be used.