Quote:
2005 NEC 392.5(E) which is currently adopted by the State of Florida ? specifically calls for fittings to change direction ? 392.5 (A), (B), (C), (D), (are) also affected by field modifications and would not be acceptable.
Victor Lombardi Acting Electrical Director
Miami-Dade County Building Department
Again, opinions vary, but I have seen a lot of differing reasons why my photos are violations.. ..
All of the states in which I am registered are on the 2008 NEC. The verbiage in 392.5 uses phrases like "or equivalent" and "other suitable".
If the manufacturer's splice plates are suitable for maintaining the structural integrity of a straight run of tray, they probably do not compromise it when used to create the 90? bend in your photo.
A single photo is not sufficient to pass judgment on a classified product. The entire installation must be judged as a completed assembly.