If I remember correctly, that is a 10-24 thread. I think a trip to the hardware store and a green sharpie would have been better than what happened here.Looks like they lost the screw.
View attachment 2577564
If I remember correctly, that is a 10-24 thread. I think a trip to the hardware store and a green sharpie would have been better than what happened here.Looks like they lost the screw.
View attachment 2577564
That's a bunch on nonsense, if the GEC is landed in the meter base, that's all that is needed. It bonds to the neutral there and no further bonding is required.I have seen a service like that except it was a underground, and they landed the GEC's on the neutral bar in the panel (water pipe and ground rods) then had s SSBJ go beck thru the hub to a ground bushing on the nipple in the meter can, then another ground bushing on the old rigid service lateral conduit stubbed up from the POCO. Neutral also bonded in meter can. Is that legal?
10-32If I remember correctly, that is a 10-24 thread. I think a trip to the hardware store and a green sharpie would have been better than what happened here.
I know regular hex screws for bonding junction boxes are 10-32, but I think the panel bond screws are 10-24 or 12-24.10-32
I have never seen a GEC landed at other than the service disconnect for a single family dwelling.That's a bunch on nonsense, if the GEC is landed in the meter base, that's all that is needed. It bonds to the neutral there and no further bonding is required.
Unless the seal is non-reversible (you have to cut it) and you consider the seal part of the "building finish" (I wouldn't), it would meet the Article 100 definition of "accessible." 250.24(A)(1) requires the GEC connection to the grounded service conductor to be at an accessible location, so certainly these POCOs that require a connection in their meter must view that as an accessible location.If it were sealed in a utility meter with these new seals they use my inspector might not see that as accessible.
It is almost always up to the utility whether they allow it or whether they require it. If they allow it but the inspector forbids it, then it can't go in the meter. But if the utility requires it at the meter, the inspector has no choice but to allow it.I have never seen a GEC landed at other than the service disconnect for a single family dwelling.
In my area with new residential construction) its a UFER rebar ground and if I am not mistaken all ufer connections are required to be 'accessible', if one pops up in a wall to be covered we leave a mudring on a stud by the ufer end connection so a blank cover can deem it accessible. The other end is accessible in the service panel. If it were sealed in a utility meter with these new seals they use my inspector might not see that as accessible.
If I had to call the POCO to unlock it or cut the lock my AHJ would have no hesitation red-tagging sticking it to the POCO.Unless the seal is non-reversible (you have to cut it) and you consider the seal part of the "building finish" (I wouldn't), it would meet the Article 100 definition of "accessible."
Why would you need access to the GEC after the install?If I had to call the POCO to unlock it or cut the lock my AHJ would have no hesitation red-tagging sticking it to the POCO.
Why would the inspector not allow it? It's permissible anywhere from the weatherhead down to the service panel. In the meter base is part of that path.If they allow it but the inspector forbids it, then it can't go in the meter.
Because the tagged meter base may be considered inaccessible.Why would the inspector not allow it? It's permissible anywhere from the weatherhead down to the service panel. In the meter base is part of that path.
It's as accessible as a ground rod with the acorn clamp grade driven below grade.Because the tagged meter base may be considered inaccessible.
Cool. I agree that it is best at the meter, or even at the weatherhead. But I've seen both POCOs and inspectors that don't allow it.It's as accessible as a ground rod with the acorn clamp grade driven below grade.
All the inspectors here laugh at the POCO that won't allow it in the meter.
Different code section applies Wayne stated its "250.24(A)(1) requires the GEC connection to the grounded service conductor to be at an accessible location". Ground clamps are not the connection to the grounded service conductor and can be listed for direct burial.It's as accessible as a ground rod with the acorn clamp grade driven below grade.
Its the OP is saying the utility is requiring it:All the inspectors here laugh at the POCO that won't allow it in the meter.
I say if it is a violation, as its open to interpretation, but sure seems like it. So if you go along with me and say AHJ say it is a violation, which it would be here. A Utility can not just decide to 'over rule' the NEC and require a code violation?, Perhaps unless the utility is also the AHJ in the town? Does NEC not 'start' well before a meter ? start at the OH splices ? So not their jurisdiction article 90 right?Local utility requirements call for the ground to be connected to the meter socket neutral.
It’s not required to be readily accessible just accessible and it’s definitely accessible in a tagged meter base, a tool removes the tag and you have accessBecause the tagged meter base may be considered inaccessible.
OK. I'll let you take it up with the AHJs who disagree. Rarely do I encounter a utility that allows the connection in there anyway.It’s not required to be readily accessible just accessible and it’s definitely accessible in a tagged meter base, a tool removes the tag and you have access
If the proof of access must be proven at a normal inspection if not inspection it fails, tool is not present and the owner cannot tamper with the meter I don't see how it would fly.It’s not required to be readily accessible just accessible and it’s definitely accessible in a tagged meter base, a tool removes the tag and you have access
Idk how it would not be accessible at the time of inspection, since poco will not come out and tag/energize a service until it’s been signed off by a electrical inspectorIf the proof of access must be proven at a normal inspection if not inspection it fails, tool is not present and the owner cannot tamper with the meter I don't see how it would fly.
An inspector challenged me on something much more accessible, it was a 12X12 pull box (several actually) that ended up too close to the drop ceiling grid, I had to open it with him standing there to prove it was accessible, and sure enough I broke the ceiling tile, he insisted on a access panel.
Where in mass do you see a GEC in a meter? I just never have seen it and it seems dumb.Idk how it would not be accessible at the time of inspection