Every gec/bonding jumper that connects to a rod/plate in mass ends up landing in the meter and it’s been that way long before 230.85, and 250.24(a)(1) says it can terminate anywhere on the supply side from the weatherhead to the service disconnect , and it can be accessed very easily and no finished materials are removed, it’s not welded shutWhere in mass do you see a GEC in a meter? I just never have seen it and it seems dumb.
On final inspection inspector checks that after the building is finished things are accessible.
Why do they check I have a 2 gang mud ring and a blank where the ufer clamp is it if its concealed in a wall?
When do they check my pull box is accessible ? final inspection
So it can be accessed.
And for final inspection I need the power on.