MrArachnid
Member
- Location
- Titusville, FL US
I think I am confused by the facts. Our engineer hit me with more motors which means I have to order more MS. Problem- I am trying to maintain uniformity with my control cabinet and I have 24 VAC from I/O Modules. The distro can't get me the 24 VAC coil on the contactors that I need but he has 24VDC in stock. There should be no reason why it would would matter whether I am applying VDC or VAC to the coil. The only difference should be that the coil can handle higher current given the lower voltage. Am I looking at this the wrong way?
I either get what I can without the lead time or rectify the voltage to the coil with a XFMR. I just don't see that I would have to.