- Massachusetts
Re: Color Re-Coding
Use what ever name you like, many people use different names at the different forums.
If these are branch circuits, that would be a violation of 210.4(D) because you have no way to identify the phase of the ungrounded conductors. If they are feeders there is no problem.So, is there anything wrong with pulling three blacks and a white to all my 208/120 panels, and three blacks and a gray to all my 480/277 panels? Just so long as I identify this scheme at all my panels?
As long as the two systems are not in the same raceway or enclosure, then the use of white and gary as stated in your post is code compliant, however if the systems share enclosures, there is a violation of 200.6(D).(D) Identification of Ungrounded Conductors. Where more than one nominal voltage system exists in a building, each ungrounded conductor of a multiwire branch circuit, where accessible, shall be identified by phase and system.This means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means and shall be permanently posted at each branch-circuit panelboard.
Don to be clear that only would apply to conductors of a multiwire branch circuit, not all branch circuits.(D) Identification of Ungrounded Conductors. Where more than one nominal voltage system exists in a building, each ungrounded conductor of a multiwire branch circuit, where accessible, shall be identified by phase and system. This means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means and shall be permanently posted at each branch-circuit panelboard.[/b]
Yeah or it could one line to line circuit and one line to neutral circuit.Originally posted by don_resqcapt19:
Bob,
Earl's post specified 3 blacks and a white. That would be a muliwire circuit.
Don
So they could black as long as they are identified.separate color coding, marking tape, tagging, or other approved means and shall be permanently posted at each branch-circuit panelboard.
Webspark the only time the ungrounded conductors are required to be identified is when there are part of a multiwire branch circuit.Originally posted by websparky:
Right OnWell also Rogers Iso systems.
Welcome to the forum Chicar, just because I argue about NEC minimums that is not how I work, I agree common sense and courtesy are a good thing!Originally posted by chicar:
Black,Red,Blue,White 120/240v Brown,Orange,Yellow,Gray 277/480v is known throughout the land and should be In forced by the N.E.C.
It is only a violation where the grounded conductors from both systems are in a common raceway or enclosure.Go easy on that white for 120 and gray for 277 as that is an NEC violation now, (see Tom Bakers post back a little way in this thread)