pvgreeze
Member
- Location
- Philadelphia
- Occupation
- Electrical Engineer
Is that specific definition defined anywhere? That 705.12 applies to everything beyond the first OCPD? Is that the same for instances where 705.11 is invoked? Looking at 705.11(A) specifically, it is clear that it defines Output Rating as "the sum of the power source continuous current output ratings" which we defined using 690.8(A)(1)(e). 705.12(A) even specifies that a Dedicated Overcurrent and Disconnect are needed (the 800A fused DS) at the point of interconnection and that this device can service "one or more power sources." So why are we disregarding that device in the language of 705.12(B)(3)(3), which states that it is "the busbar," not "any busbar" and includes very specific language for a warning label regarding the calculations of the ampacity of devices on that "equipment," not any equipment associated with the "one or more power sources".690.8(A)(1)(e) applies to the circuit from the AC-side of a single inverter to the first OCPD. 705.12 applies to everything from that OCPD to the utility.
Even staying in 705, 705.28(A) defines the maximum current to be the continuous output current rating of the power production equipment (4*144.3 + 36.25 = 577.2A) and assuming we can invoke 705.30(B) that the OCPD should be 800A, hence the 800A fused DS in the switchboard. The "other than generator systems" line in 705.30(B) is unclear though...
I would agree that 705.12(B)(3)(3) would be invoked if that 800A fused DS did not exist for some reason, which would be in violation of 705.12(A), but that is the device that is being installed in the switchboard. If there is clear language that "690.8(A)(1)(e) applies to the circuit from the AC-side of a single inverter to the OCPD. 705.12 applies from everything from that OCPD to the utility" then I understand that interpretation, but I'm not sure where that specific definition is coming from.