Got it, thank you!The SE120K-US has 144.3A maximum rated output current, which takes a minimum 180.4A OCPD, which rounds up to 200A. There is nothing "bizarre" about that; that it does not land directly on a standard OCPD size is the rule rather than the exception; most inverters don't and there is no reason why they should.
I have a hundred or more commercial PV systems under my belt in many different AHJ territories and every single one of them evaluates my PV AC combiner panels for compliance with 705.12(B)(3)(3).