Me again. I have to run a 3ph feeder from a fused switch to a M/L panel in a commercial space. As there is no tenant yet, we have no load calcs, but I'm 99% sure it will never approach 225a.
We're also running a 200a 1ph feeder and panel in the same space, so I'm doubly sure we'll not see anywhere near 225a on the 3ph. Both are from a high-leg transformer bank, by the way.
How do I determine whether to price for and install 250 or 300 MCM aluminum? The conduit is 4" EMT, both because of downsizing from the original 400a panel, and in case of future needs.