The temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor, or device. Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both.
You need to read it again, especially this partI am sorry, I know a few complain about me at times on this site, others seem to like what I have to say, everyone is different and that is part of life. I am not trying to badger anyone, but please tell me how 110.14(C) has anything to do with ampacity adjustment? Ampacity adjustment is for conductors not terminations, 110.14 is not even about conductors, it is about terminations
Nothing in there says anything about how or where to start with ampacity adjustments - it basically says the conductor can not be less then the smallest conductor permitted on the terminal per the terminals temperature rating, but does give permission to adjust the conductor starting at the conductor rating if it is higher then the termination rating.
After that read 110.14(C)(1) and notice how many times is specifically talking about "conductors', you can't have a termination without a conductor and if you do you don't need to worry about the insulation rating anyways.Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both.
Okie dokieYou need to read it again, especially this part After that read 110.14(C)(1) and notice how many times is specifically talking about "conductors', you can't have a termination without a conductor and if you do you don't need to worry about the insulation rating anyways.
You stated that the permission to start a conductor ampacity adjustment with a higher insulation rating than the termination "is not exactly stated in one simple sentence in one code section", and I showed you where it is, go with it and don't loose any more sleep over it.
Roger
Are we on the same page? I expect someone like you already knows this but maybe we are not talking about the same thing here causing some confusion.
It is not exactly stated in one simple sentence in one code section.
310.15 applies to the conductors - we make adjustments from 90 degree values if we have 90 degree insulation.
However after making adjustments we still must have a conductor no smaller then what is called for in the 60 or 75 degree columns of ampacity table for the sake of termination temperatures. That gets us back to what was mentioned about 110.14 Two different ampacities are required for same conductor in different portions of the conductor - the higher ampacity is what must be used, but don't know of any possible adjustments to termination ampacity, just to conductor ampacity only as it applies to it's insulation.
You can have a situation where ampacity adjustment says you can have a 6 AWG conductor for the temp rating of the insulation, but same application may need 4 AWG for the termination temperature - so in that case you still must use the 4 AWG.
Why do you think anybody is contesting what he said?I agree with kwired explanation. The "termination" degree rating is strictly the ratings of the equipment and its terminations (mechanical lugs and such) under UL testing. The conductor size acts as a heat sink which is why there is a degree listing in the first place.
I don't see anybody confused about the word termination.I think the confusion is in the interpretation of the word termination.
There is 90 deg terminations, just not very common.Since there is no 90 C listed equipment there wouldn't be a need for this table if not for the use of 90 C wire adjustment and correction factors.
Roger
Exactly!!!Last sentence of 110.14(C) I interpret as the clearest distinction that you can apply correction factors at 90 C
As uncommon as you mention 90 C terminations can be.......... I didn't even imply they were uncommon if fact they are fairly common, my point is there is no 90 C EQUIPMENT . Don't matter what the Terminations (LUGS) are rated for above 75 C if the gear is 75 C .Which is why anything over 100 amps is treated as 75 C.
If you say so. :roll:kwired meant you could not use correction factors @90 C for wire only rated at 75C such as USE that does not have a USE-2 stamp on in making it also 90 C
I stand corrected. For the purposes of # CCC adjustment, we use the 90 deg column. Sorry for the confusion I created. :? Hey let's start a new argument. When do you count the neutral as a CCC in a network? :lol:
To summarize it:
Neutral counts as a CCC, if it is a mandatory part of the return path for the current. Or if nonlinear/harmonics currents account for a major portion of the loads.
Examples where neutral is a "mandatory part of the path for the return current":
1. Phase-to-neutral single phase circuits
2. Two phases + a neutral, from a three-phase main circuit, used with phase-to-neutral loads on each. 100A on phase A + 100A on phase B requires 100A to return on the neutral when phase C is not present.
Examples where it doesn't count.
1. Three phase circuits from a WYE system with linear loads, no matter what the imbalance (if any)
2. Split-phase circuits from a single phase system with linear loads, no matter what the imbalance (if any)
3. Where it is only connected for instrumentation purposes, and doesn't ever carry significant current.
The condition of nonlinear/harmonic loads is very obscure and difficult to objectively know. The follow up question is, given an oscilloscope graph of the voltage and current for that particular load, how can one know for sure if it neutral would have to count as a CCC?
Exactly, which is why it's so heavily debated. Definitely would consider electronic ballasts a non-linear load. I've gotten in debates about this many times. For convenience receps, we might as well consider it non-linear because anything could be plugged in. Just about all devices now-a-days produce non-sinusoidal signals.
On a 4-wire, 3-phase wye circuit where the major portion of the load consists of nonlinear loads, harmonic currents are present in the neutral conductor; the neutral conductor shall therefore be considered a current-carrying conductor.