Do conduit straps need to be UL listed ?
Agreed, even a bent over nail.As far as I know, No they don't. You can use a tie wire to strap the conduit.
An accessory such as a locknut, bushing, or other part of a wiring system that is intended primarily to perform a mechanical rather than an electrical function
There's no requirement for one to use a fitting to secure or support. IMO it does not matter whether the strap is listed or not....
I am still left with an answer of I don't know if straps are required to be listed.
I totally agree.There's no requirement for one to use a fitting to secure or support. IMO it does not matter whether the strap is listed or not.
What about support by a framing member? Does a framing member need to be listed for the purpose?
A bit of common sense goes a long way... but when you have Code saying cable ties are okay in certain articles, people seem to lose their [common] sense when it comes to other articles. If you secure or support a metal wiring system to the bottom of structural ceiling elements with cable ties, what's gonna happen if there's a fire?...
I think not.
That is where "approved" comes in to play. Metal strap with short screw into a wood framing member may also come down long before the structural member is significantly weakened by the fire, approved in that instance may mean a longer screw is necessary.A bit of common sense goes a long way... but when you have Code saying cable ties are okay in certain articles, people seem to lose their [common] sense when it comes to other articles. If you secure or support a metal wiring system to the bottom of structural ceiling elements with cable ties, what's gonna happen if there's a fire?
I thought a strap met the definition of a fitting, but the CMP did not agree.If you look at XXX.6 in every raceway article it says applicable raceway type, factory elbows, couplings and associated fittings shall be listed.
Art 100 definition of Fitting.
Is a strap a fitting? maybe.
8-5 Log #2239 NEC-P08 Final Action: Reject
(342.6 Exception (New) )
________________________________________________________________
Submitter: Donald A. Ganiere, Ottawa, IL
Recommendation: Revise as follows:
342.6 Listing Requirements. IMC, factory elbows, and couplings, and associated fittings shall be listed.
Exception: Raceway support fittings and accessories shall not be required to
be listed .
Substantiation: The Article 100 definition of “fitting” seems to include raceway supports. Many of the commonly used raceway support straps, clamps, and other items are not listed.
Panel Meeting Action: Reject
Panel Statement: Conduit support accessories are not considered “Fittings”. Sections 300.6 and 300.6(A) require support hardware to be constructed of materials suitable for the environment for which they are to be installed.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12
(blue text = proposed new text)
You should realize by now that our English is not the same English the CMP members use. :slaphead::lol:I thought a strap met the definition of a fitting, but the CMP did not agree.
Now how do you tell a stubborn inspector that even though many of them are listed, they are not required to be. If I use a strap listed for 3/4 EMT to support 1/2 RMC is that a problem? I don't think so. Not that I had that exact problem that I can recall but have had similar issues before.I thought a strap met the definition of a fitting, but the CMP did not agree.
[/COLOR]
Show them the ROP.Now how do you tell a stubborn inspector that even though many of them are listed, they are not required to be. If I use a strap listed for 3/4 EMT to support 1/2 RMC is that a problem? I don't think so. Not that I had that exact problem that I can recall but have had similar issues before.
I used some 1" one hole EMT straps to support SER cable
SE cable? hmy:
The cable caught fire right as I was carrying it out of the supply house. Never even got a chance to install it.
What's it like to be so infallible?I used some 1" one hole EMT straps to support SER cable because the supply house was out of the plastic SER staples. Good thing I didn't have that one inspected.
Always wear your gloves.