ohmhead
- ORLANDO FLA
Well thanks Roger , dont take me the wrong way i do listen to my wife sometimes , i did learn a lot it was fun cant wait for the next debate .take care Roger
but only after you've filled the conduit full of wire.
I agree with drilling a hole for securing,but disagree with altering it for the purpose of adding a conduit. I believe that would alter the listing.
Well yes but it also says unless specs are more stringent then the nec min standards we go by specs not the nec
They would laugh at us if we used the ul white book wrote a R F I to drill a hole in a fitting to support it
iwire said:The white book is one of the primary references that inspectors use to determine the suitability of equipment for a particular installation.
The UL listing only says the product met a specific standard when it was shipped from the factory. The UL listing says nothing about the product actually having been applied or installed correctly; UL leaves that judgment up to the AHJ.In any case the drilling of the condulet would put the UL listing in limbo and only a UL field inspection would/could resinstate that.
You miss my point. The only person that can judge that the product as been actually been applied correctly is the AHJ. The statement from UL, about modifications, admits their listing, and the instructions it requires, helps with but does not replace AHJ judgment.The product is submitted for testing with all the manufacturers literature and instruction and UL does review it and asks for corrections and additions to comply with the listing. The instructions also bear the UL listing and labeling requirements. In case of multiple listing, such as instruments whre the instructions can cover multiple type of listing, the instructions detail how to comply with XP, NEMA 4 or IS requirements.
If, I drill a hole for a custom KO in a fire alarm control panel in which there wasn't a factory stamped KO, does this violate the UL listing?
I can't see how that would violate the UL listing. If there are no factory KO's then how are you supposed to install any wiring? Nonsense I say!!
The UL listing says it left the factory in proper condition. The UL listing is not applicable to the holes that you field cut. It is up to the AHJ to decide if your field cut holes negatively impact the installation/application of equipment. For example: Does UL require all field cut entrys into a UL Type 1/3R/4/12 enclosure to be made in the same way?I can't see how that would violate the UL listing. If there are no factory KO's then how are you supposed to install any wiring? Nonsense I say!!
This falls along the line of you buying junction boxes that come without any holes at all and drill your own.
its not a box
its a conduit body
A wireless system of course...:grin:
Yes, and I have to comply with 225.22.