Contactor that doesn't hum?

Status
Not open for further replies.

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Here's what Siemens has to say on the topic:


So per the above, if the contactor 30A rating is a thermal limit, and the make/break limit is over 40A, you could wire the two poles in parallel, not series, to increase the thermal limit. Series wiring is to increase the voltage limit or handle DC.

Cheers, Wayne
 