chris68
- Denver, CO
Re: cooktop / oven
Roger, it's my contention that a neutral is required and it shouldn't be any smaller than 70percent leading to a range recepticle. Seems like 210.19 A 3 ex 2 addresses this by saying, "The neutral conductor of a 3-wire branch circuit supplying a household electric range, a wall mounted oven, or a counter mounted cooking unit shall be permitted to be smaller than the ungrounded conductors where the maximum demand of a range 8.75kW or more rating has been computed according to Column C of Table 220.19 but shall have an ampacity of not less than 70 percent of the branch-circuit rating and shall not be smaller than 10 awg."
Your comment that a neutral isn't required would seem to contradict the code section I cited.
JimWalker's comment seems to be a slightly different scenario. Sounds like there was nowhere to terminate a neutral to in a cooktop and the inspector insisted on seeing 4 wires entering and leaving the closest jbox where his taps fed from.
a.wayne3@verizon.net, what was your inspector's verdict?
Earlier when I asked about the branch circuit ampacity...I didn't realize ovens are continuous loads. Shows you how often electricians crank up the oven for 3 hours or more, huh?
Some conversations where discussing the theory concerning if a neutral would carry a load or not. I was able to borrow my friends 1999 NEC handbook and it offers the following comment on ranges: "On modern ranges the heating elements of the surface units are controlled by five-heat unit switches, The surface-unit heating elements will not draw current from the neutral unless the unit switch is in one of the low-heating positions. This is also true to a greater degreee as far as the oven-heating elements are concerned, so the maximum current in the neutral of the range circuit seldom exceeds 20A. Because of that condition, Exception No. 2 permits a smaller-size neutral than the ungrounded conductionrs, but not smaller than No. 10."
NECBuff...the title of article 220 is "Branch, Feeder, and Service Calculations." On a new installation I believe you would still need a neutral as well as a ground. Why wouldn't this be a requirement of 210.19 A 3 ex 2 if for no other reason?
[ July 11, 2004, 11:04 AM: Message edited by: chris68 ]