Katessa Harris
New User
In a house that is not new construction, is there a way to tell if it has been properly grounded?
Katessa Harris said:In a house that is not new construction, is there a way to tell if it has been properly grounded?
nakulak said:I wanted to reply to the other thread with this same name, but it was closed.
The code does not have a maximum limit on the grounding resistance. What it says if a rod, pipe or plate electrode is more than 25 ohms an second electrode must be added. Then you go home.Lxnxjxhx said:There are many previous posts on how to measure ground resistance. The specification limit seems to be < 25 ohms.
Lxnxjxhx said:If the NEC is about safety, I'd think where it is reasonably practical to do so there'd be performance testing required. Is this wrong?
The connection to earth has very little to do with electrical safety in standard building wiring installations. 250.56 is the only place the 25 ohm rule showes up and it only applied to rod, pipe (driven pipe, not water pipe) and plate type electrodes. It only says that if you don't have 25 ohms or less with the first electrode you install a second. There is no requirement to try to get down to the 25 ohms.Lxnxjxhx said:If the NEC is about safety, I'd think where it is reasonably practical to do so there'd be performance testing required. Is this wrong? Is testing of new work just "good practice?"
It doesn't seem to me that following proper procedures, even meticulously, always guarantees the desired result.
Not possible. If the GFCI trips with the internal test button it will trip with a 60mA external ground fault. All the internal resistor does is let some of the current flow on a path that is not sensed by the current sensor.Lxnxjxhx said:Now, I recall that while the outlets did actually supply electricity the GF did not trip with a 60 mA fault from L to G. The test button did work because it connects an internal resistor.
The instruments made for this purpose use frequencies other than 60 Hz, or multiples thereof, because there seems to be a lot of ground noise at various freqs. I think there are some favored, "quiet", freqs. commonly used.
This 60 Hz prohibition kind of puts a damper on homebrew ground testers.