That's what I'm trying to fathom out. The why.
The substitution of AL for CU at larger feeder sizes comes with it the proper precautions due to the greater expansion and contraction of AL, which loosens terminations. Common examples:
1. Aluminum alloy conductors shall be compact stranded conductors.
2. Aluminum conductors shall terminate on a compression lug or compression adapter.
3. Oxide-inhibiting joint compound must be applied on the aluminum conductor during termination.
Using AL for branch circuits may be done if the cost difference is there, but it typically is not done. Branch circuit conductors have higher likelihood of casual changes over time purposely loosening and tightening - precautions are often forgot. Forgetting has high arc flash hazard concerns. Furthermore, most mechanical equipment is listed based on CU terminations (due to the vibrating nature is my guess); thus, motor branch circuits are especially CU.